Ask Experts Questions for FREE Help !
Ask
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #1

    Jan 21, 2012, 03:50 PM
    Sub panel question
    I was thinking of running a 60 amp sub panel to a barn about 75 feet from the main panel. I've read that in a sub panel ground and neutral must be separated. However, can I just run three wires (hot, hot, neutral) to the barn, and drive a grounding rod at the sub panel, and leave the ground and neutral bonded in the subpanel? Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 22, 2012, 04:46 AM
    No, the new feeder must be 4 wire, with two hots, one insulated neutral and one insulated equipment ground conductor.

    The three wire method is no longer allowed.
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #3

    Jan 22, 2012, 11:13 AM
    Is there a particular reason this is no longer allowed?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 23, 2012, 03:31 AM
    4 wire system is safer than 3 wire.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical Service Panel question, help please [ 13 Answers ]

My house electrical service panel (38 years old) that is divided into an upper section and a lower section. The upper section is fed from the Extermal Meter box which passes through conduit to the service panel. There is NO breaker or switch in the meter box that I can see. The service panel...

Second sub panel and conduit question [ 3 Answers ]

Hi all, New to this forum and finding lots of great advice. I'm planning on adding a 100A sub panel to my garage workshop. The house has 200A service and the main panel is located in the garage. The plan is to use a 125A main lug panel fed by two #2 copper for the hot feeder legs, a #6...

Question about an electrical panel [ 2 Answers ]

I am in the plannnig stage of a basement remodel. I checked the breaker box and found that I have 2 circuits currently in the basement. One is for 8 overhead lights and one is for 4 GFI outlets located around the basement. My question is, there are 5 open slots in the panel that I could use...

Sub-panel AMP amount question [ 4 Answers ]

Hello, I have a 150 amp main and a full 150 amp circuit breaker box with a number of doubled 20 amp breakers. Can I still add a sub panel? If so, how does one calculate the maximum amount in amps of such a sub panel? -Terry

Another flat panel question [ 4 Answers ]

I have been reading up on 19' flat panel monitors in anticipation of buying one. I am a little confused by the native resolution thing. I am over 50 years old and a little worried about text and picture imge size as I do a lot of online reading and a fair amount of photo processing. If I understand...


View more questions Search