    Sub panel question
    I was thinking of running a 60 amp sub panel to a barn about 75 feet from the main panel. I've read that in a sub panel ground and neutral must be separated. However, can I just run three wires (hot, hot, neutral) to the barn, and drive a grounding rod at the sub panel, and leave the ground and neutral bonded in the subpanel? Thanks
  • Jan 22, 2012, 04:46 AM
    tkrussell
    No, the new feeder must be 4 wire, with two hots, one insulated neutral and one insulated equipment ground conductor.

    The three wire method is no longer allowed.
  • Jan 22, 2012, 11:13 AM
    Kyle_in_rure
    Is there a particular reason this is no longer allowed?
  • Jan 23, 2012, 03:31 AM
    tkrussell
    4 wire system is safer than 3 wire.