    Main disconnect breaker kAIC ratings?
    Can I use a 10 kAIC main breaker in a main disconnect or does it have to be a 35 kAIC main breaker? I have a 10 kAIC, 225 amp breaker on hand, and I did not want to have to buy a new 225 amp 35 kAIC breaker if I did not have to. My indoor load center has a 10kAIC, but the outdoor, main disconnect, the one at the pole is currently 35kAIC. This is the one I would like to replace. All panels and breakers are Cutler Hammer. I have the new 225 amp load center inside (not hooked up yet) and the POCO already upgraded the transformer and the wire from the pole to the meter. I am upgrading the wire from the meter pole to my house with 4/0 aluminum. The main breaker disconnect at the pole, under the meter, is rated for up to a 225 amp breaker according to Cutler Hammer's website and the label inside the disconnect enclosure. It currently has the 35 kAIC breaker in it right now. I have a 10 kAIC, 225 amp breaker on hand that I would like to put in there, however I did not want to have it put in the main disconnect, if it needs to be a 35 kAIC like is currently in there. Thanks for the help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 1, 2007, 01:47 PM
    Not knowing how the 35KAIC rated main breaker came to be, you need to check with the utility for the KAIC rating of their system.

    I would have to assume that the 35 KAIC was required at the time of installation.

    There is a chance that only 10K is needed, and the installer had the 35K on hand.

    Most residential services only need to be rated 10KAIC, but, again, this is dictated by the utility transformer.

    Check with the utility, and do as they require.
    gerlon's Avatar
    gerlon Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 5, 2012, 09:26 PM
    If your breaker is intended for residential application, 1o kaic is enough, higher kaic applicable only for industrial use.
    gare's Avatar
    gare Posts: 1, Reputation: 1
    New Member
     
    #4

    Dec 5, 2012, 08:34 PM
    It is as TK states, it is predicated by the available inrush at the point of connection. The utility may provide the KAIC available at the disconnect, but sometimes they will only provide the KAIC on the secondary side of the transformer. If this is the case, you need to calculate what can reach the fist protection point. Faults dissipate quickly overlong wire runs.

    Residential installations could easily require 22kaic if they are the first home after the transformer feeding them.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #5

    Dec 6, 2012, 05:37 AM
    As stated the Utility "must" provide to you the available short circuit at the secondary of the transformer...
    Then, if you can tell us what that is... and then tell us if there is a single transformer and the voltage (for residential it's normally 240V), the size and length of the cable to the first disconnect and whether it is in free air or conduit, the size and length of the cable to the next disconnect or panel and whether it's in free air or conduit...
    Knowing the above, the short circuit at the various locations can be calculated with reasonable accuracy.

    There is no rule of thumb here!... utilities have been using energy efficient transformers more an more often that can provide much higher short circuit levels so you must contact the utility before you can go any further.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Main breaker panel [ 1 Answers ]

Hi, I'm looking for a 100 or 125 amp 30 or 32 space main breaker panel(not a mlo) and have been unable to find one. Can some one tell me where I can get one with the main installed? Thanks Jim

200 amp breaker/disconnect [ 2 Answers ]

I'm needing wiring help. I am wiring a mobile home and at the service pole I'm not wanting to hang the 200 amp breaker box since it's over one foot long and would like to hang a much small box w/ only a lone breaker or disconnect before going to the 200amp breaker panel mounted else where. ...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Main breaker and main disconnect [ 2 Answers ]

What I have is a home built in 1960 moved in 2 years it had a meter hanging from the rear of house with no main, 240v 50amp circuit to stove, 240 30amp to dryer, 5 breakers for the rest of house 1 20amp and 4 15amp. What my plan is to replace the meter housing and put a g.e. 200amp Disconnect on...


View more questions Search