    What size wire ?
    What size wire must be run for 6 - 30amp sub pannels 350' away from 100 amp main?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Dec 20, 2011, 12:17 PM
    Will the six additional panelboard be in the same building or are they going to be in outside buildings?

    You do understand that you are going to be pulling a maximum of 180 amps away from a 100 amp main panelboard.

    Without additional information from you, I would speculate that you need 4 ea. of #8 copper conductors. This is ONLY if the conductors are inside the same building.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Dec 20, 2011, 02:53 PM
    I do not know why if the wiring is inside or outside would make a difference regarding voltage drop.

    To do voltage drop calculations, need to know the supply voltage and the actual load in amps or wattage.

    Assuming 240 volts at 30 amp load, #4 copper is needed.

    If 120 volts at 30 amps, then #1 copper wire is needed.

    Can you explain further why 6-30 amp feeders are needed to go 350 feet?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Dec 20, 2011, 07:27 PM
    Knowing whether the wiring is inside or not will further define the method for grounding at the secondary panelboards.

    T.K. What wire size calc are you using? I set mine to 240/30 using copper. The distance was 350' and it comes up with #8 conductors (voltage drop of 6.8%)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

What size wire do I need to run to get a 100amps. 225ft. using direct burial wire? [ 5 Answers ]

What size wire do I need to run to get a 100amps. 225ft. using direct burial wire coming from a 200amp. Service? Any info. Would be appreciated. Regards, Garry

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...


View more questions Search