    200 amp main to a 100 amp sub panel.
    I have a 200 amp main in the garage that is completely full. I want to add a 100 amp sub panel right next to it,(a few feet away) so I can add some wiring to the attic and basement. What size cable is required to connect the 200 to the 100 sub indoors just a few feet away?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 19, 2011, 08:20 AM
    You may use either #3 copper THHN or #1 aluminum XHHW .
    ibkorthy's Avatar
    ibkorthy Posts: 3, Reputation: 1
    New Member
     
    #3

    Oct 21, 2011, 05:18 AM
    Is it OK if I already bought 2224?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 21, 2011, 06:13 AM
    I will assume the #2 is aluminum, which you may use only if you protect it with a 90 Amp breaker.

    Would have been good to mention that in your original question.
    ibkorthy's Avatar
    ibkorthy Posts: 3, Reputation: 1
    New Member
     
    #5

    Oct 21, 2011, 10:00 AM
    I didn't buy it until my question went unanswered for 2 days, The electrical guy at Home depot said 2 2 2 4 would be the way to go. 100amp breaker. I'm only running 2-15amp and 1-20amp circuits from it. I have an electrician friend coming to install it so if he says its not right I will toss it. I only needed 6 feet of it. He is out of state hunting and I can't get in touch with him until sat. Was hoping to have everything here ready to go for him. Thanks for the reply. Much appreciated.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Oct 21, 2011, 01:09 PM
    Clerks in stores should not be giving advice unless they have a license for that trade. And he is incorrect on the 100 Amp breaker on this feeder with #2 Al to a subpanel.


    What I see for date/time stamps is you posted a question on 10/19/11 at 11:05 AM and me answering the same day at 11:20 AM. Is that what you see?

    Since you have an electrician installing the feeder, any liability or code violations will fall under his license.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a 100 amp main panel and I want to feed a 200 amp main lug. [ 1 Answers ]

The panel I have now is a 100amp main breaker and I still want the ability to keep some of the circuits that it currently has in it. I am putting the 200amp main lug in my house and was wondering if it is safe to put a 100amp break in my main panel to feed the 200 amp main lug panel and if so...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

200 amp main panel: 2 100 amp subpanels? [ 1 Answers ]

I was asked to by a homeowner to help with a wiring project. She has 1 200 amp main panel and 1 100 amp subpanel. Both are full yet she needs more circuits for a bed n' breakfast. Can another 100 amp subpanel be installed?

100 amp sub panel from 200 amp main panel [ 2 Answers ]

We have a 200 amp main panel. We added another floor and decided to add a new sub panel of 100 amps. Is this OK? Should the wire gage be different from 100 maps? Your help is appreciated.

100 Amp Subpanel from 200 Amp main panel [ 2 Answers ]

I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...


View more questions Search