    asabear's Avatar
    asabear Posts: 1, Reputation: 1
    New Member
     
    #1

    Sep 14, 2011, 12:23 PM
    Can I tie a single wire to a double pole breaker.
    Can I tie a single wire(120V) to one side of a double pole breaker. Amperage of the breaker matches the load I need, but it is a double pole and I don't have two singles to replace it with.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Sep 14, 2011, 03:04 PM
    I don't see a problem.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Sep 15, 2011, 05:49 AM
    I'm no sure what you are asking.

    Do you mean, can you take a double pole circuit breaker and attach it to the bottom of the bus bar so that only one pole of the breaker is attached to the panelboard?

    If so, then the answer is "No." The reason would be that you are not using the circuit breaker per the manufacturer's instructions.

    The manufacturer's design calls for both poles of the breaker to be latched onto the panelboard.

    Also, a two pole breaker is not listed for use as a single pole breaker.

    You can probably pick up a single pole breaker for $20. Or less at any number of hardware stores.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Sep 15, 2011, 04:23 PM
    Multiwire circuits use 2 pole breakers, or should by current code. This is one circuit, Only downfall is you lose a space?
    TK?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Sep 16, 2011, 02:34 AM
    I see no problem using one pole of a two pole breaker.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Sep 16, 2011, 07:21 AM
    If the breaker is installed properly (using two positions) I agree. But if one pole is left hanging off a phase bus, I believe that would be a problem, correct?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Sep 16, 2011, 12:14 PM
    Of course,

    Quote Originally Posted by donf View Post
    But if one pole is left hanging off a phase bus, I believe that would be a problem, correct?
    However, I do not see that is what suggested.

    Besides, the panel cover would not fit, and most, if not all, panels have an obstruction of some sort at the bottom of bus bars to prevent that from happening.

    While you may be thinking outside of the box, in a three dimensional world, your encroaching into the fourth dimension.

    While I may be able to make the case the usage of only one pole of a two pole breaker may be a UL listing violation, as long as the panel is labeled correctly and accurately, I have seen much worse done.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Sep 16, 2011, 12:19 PM
    Thanks, I was just asking.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to wire a 20 amp double pole breaker using 10/3 copper wire [ 1 Answers ]

I have a water pump I would like to wire for 208 /220v. I have 10/3 copper wire. I need to wire the circuit breaker for the 208 / 220 v and connect the pump.

I am converting to electric. Will 10/3 wire work? Single or double 30 amp breaker ? [ 1 Answers ]

I am converting to electric. Will 10/3 wire work? Single or double 30 amp breaker ? The heater is 4500/4500 240V

How do I wire a 10/2 wire to a double pole Breaker for 240 V? [ 6 Answers ]

I have recently baught a construction heater to wire into my garage. When speaking to the electrician at the store, he gave me all the advice my friend (who is a master's electrician) did. When I got home, I noticed that the wire he sold me to connect to a double pole Stab-lok 30A breaker was a...

Double wires on a single wire breaker [ 3 Answers ]

Hi, My home inspector put the following in my inspection report and I would like to know if anyone know the possible solutions, including the lower cost ones. Also, does this create any danger or fire hazard? * the two improper double feeds in the sub panel in the Laundry where two...


View more questions Search