    Sec cable sizing
    I am upgrading from a 100 to 200 amp service and will be upgrading my sec cable to a 2/0 or 3/0 thhn. Ive been told that nec permits downsizing of the neutral wire. Is this true and if so what size is acceptable?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 9, 2011, 02:37 AM
    If calculated, the neutral can be no smaller than 70% of the rating of the circuit.

    For the live conductors, #2/0 copper and # 4/0 aluminum is allowed for 200 Amp.

    SEC Cable has a full size neutral.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cable sizing calculation formula [ 7 Answers ]

How can I calculate the cable size for given load current? With out using any tables or charts.

Earth wire cable sizing [ 3 Answers ]

Hi , Im mike, 29 years old, I live in Mauritius. I would like to know how to size my eathing wire since my supply wire is 6 mm2. Thanks

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Shower cable sizing [ 1 Answers ]

If I have a steam room shower, that is run off water, but I need an electric cable to feed the steamer and the light inside, the shower is 3KW and in an en suite bathroom. What size cable and what size fuse would I need??


View more questions Search