  • Sep 8, 2011, 08:54 PM
    rams05
    Sec cable sizing
    I am upgrading from a 100 to 200 amp service and will be upgrading my sec cable to a 2/0 or 3/0 thhn. Ive been told that nec permits downsizing of the neutral wire. Is this true and if so what size is acceptable?
  • Sep 9, 2011, 02:37 AM
    tkrussell
    If calculated, the neutral can be no smaller than 70% of the rating of the circuit.

    For the live conductors, #2/0 copper and # 4/0 aluminum is allowed for 200 Amp.

    SEC Cable has a full size neutral.