    Can I twist 2 or 3 neutral together and put them in one slot
    OK lets say I have a subpanel and I ran out of spaces from the neutral bar can I twist 2 or 3 neutrals together and put them in one slot?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 20, 2011, 02:31 AM
    No. You may leave the bar with one wire and splice the others onto it.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Aug 20, 2011, 04:30 AM
    Quote Originally Posted by franco1 View Post
    ok lets say i have a subpanel and i ran out of spaces from the neutral bar can i twist 2 or 3 neutrals together and put them in one slot?
    No you cannot. Nor can you pigtail one neutral to several others.

    You CAN however do this with ground wires. Typically you can put two or three ground wires in the same terminal hole, but this does not apply with your sub-panel since the ground and neutral bars are separate.
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #4

    Aug 20, 2011, 06:25 AM
    tkrussell can you explain that for me splice the others onto it?so you saying is OK to splace the neutrals and use one hole if I have only one left and several neutrals?
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #5

    Aug 20, 2011, 06:52 AM
    tkrussell you saying splace the neutral and leave one just a bit loger that the others and s crew it in the only one hole left?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Aug 20, 2011, 08:06 AM
    If the circuits originate from different breakers this is not an option. The neutral pigtail will get overloaded since it will be carrying the return current from multiple circuits.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    Aug 20, 2011, 08:23 AM
    How about a larger neutral bar, or if allowed, add a second?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Aug 20, 2011, 11:19 AM
    Actually there should be no reason to run out of neutral space in a sub-panel. There should be plenty of space considering that you would be putting in an additional ground bar to keep the grounds and neutrals separate.
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #9

    Aug 20, 2011, 01:19 PM
    Thank you guys for you help.My brother and I own different units that we are wiring and I wasn't here when they put the panels for each unit, and each panel have 4 spaces for breakers and one little bar for neutrals and I thought that I that it will be fine to put the neutrals and grounds in the same bar since is only one bar,but now I put an other bar for the grounds. Thank you again.I have a doubt about something in my neighbor house have subpenal and have a log bar and the top part has neutrals and the bottom part has the grouds is that OK? Or needs a different bar also?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #10

    Aug 20, 2011, 05:24 PM
    They need to be separate. The Ground Bar Bolts directly on the panel, The Neutral is separate and Isolated from Ground.
    How many wires are coming into the Panel? 2 hots, a neutral and ground?
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #11

    Aug 21, 2011, 12:00 AM
    Yes is 2 hots and a neutral
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #12

    Aug 21, 2011, 06:42 AM
    Since you added the ground bar, do you have enough places for your neutrals?
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #13

    Aug 21, 2011, 10:37 PM
    Yes I have enough spaces for the neutras.
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #14

    Oct 14, 2011, 08:07 AM
    Hi stramando. Is 2 hots and a bare wire. I know that they need to be separate but, my question is why? OK this is what I have 3 phase panel and this panel is going to feed a 240 sub panel but, they only run 2 hots and a bare wire, I told them that we need another wire and they say is OK because the type of transformer they using.So and the sub panel I assuming that the bare wire is the neutral in this case can I put my neutrals and ground wires in the same bar since they din't run a ground wire? They say the neutral is grounded.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #15

    Oct 14, 2011, 08:49 AM
    Franco,

    You are not making sense at least to me anyway. Can you please take pictures of the site and attach them to this thread.

    If this is a residence, then I seriously doubt that you have a 3 phase installation.

    Does your main service panelboard have an orange conductor going to the "B" buss and then two more going to other power buss-es? Plus Neutral and Ground?

    I suspect that you have a single phase system (2 Hots and 1 Neutral) You need Neutral so that the 120V requirements can be met.

    Regardless, you must use a four wire feed to the secondary panelboard. Also, at this panelboard, Neutral and Ground must be isolated.

    If you plan on using 120V, you must have a neutral bus.
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #16

    Oct 14, 2011, 09:35 AM
    Hi donf thank you for you help, I will post a picture.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #17

    Oct 14, 2011, 04:15 PM
    Stanforty, are you saying you can't have 1 wire on a breaker and have 2 hots connected with a wirenut.

    What would you do If you had a conduit below the panel for a receptacle below, and you have a conduit leaving the top of the panel feeding the rest of the room, Are you saying they have to be on 2 breakers. Just curious, you seem sharp on code as does TK, and others here.
    I have seen neutral bars lacking room.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #18

    Oct 14, 2011, 05:19 PM
    No, I was only referring to neutrals.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you put the ground and neutral in the same bar in the subpanel [ 3 Answers ]

Can somebody tell me what would happen if I put the groud and neutral in the same bar in the subpanel?

Can you put a switch on the neutral. [ 2 Answers ]

I have a 200 amp service panel fed by a power company. From this power pole (the meter), the power runs 700 feet to my house. First the power goes through a disconnect box with a manual large lever (it has three settings: Power company, off, and generator). And then the power goes into my house...

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you