    Can you put the ground and neutral in the same bar in the subpanel
    Can somebody tell me what would happen if I put the groud and neutral in the same bar in the subpanel?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 13, 2011, 03:12 AM
    This will be confusing and difficult to understand by novices.

    The neutral conductor, while grounded and cannot measure voltage, is a current carrying conductor. Using a volt meter will show zero volts +/-, but using an amp meter will show the current being used by that load served by that circuit.

    A neutral/ground connection has the serious potential of sending current out on the grounding conductor to the exposed metal frames of devices and appliances and will be a shock hazard.

    Loose connections in wiring and more likely appliances will cause arcing and be a fire hazard.

    Will increase the impedance of the grounding conductor, and in the event of a short circuit may not allow the short circuit current to flow properly and trip a circuit breaker in time to prevent a fire.

    Don't do it.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Aug 14, 2011, 07:26 AM
    Very often you do not have a choice, given the length of wire, or access to the neutral and ground bar. In the main panel, the neutral and grounds are not isolated, and putting them in the same bar or not isn't a real issue. But in a sub-panel, the neutral and the grounding bars (buss) are not connected. The neutral is isolated from ground and the ground is bonded to the panel. Look in most any main panel and you will see both the ground and the neutral sharing the same buss.
    franco1's Avatar
    franco1 Posts: 26, Reputation: 1
    New Member
     
    #4

    Aug 15, 2011, 11:09 AM
    Thank you very much.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Subpanel ground and neutral are on the same bar [ 7 Answers ]

Hi, I have a subpanel where the ground and neutral are the same bar. My understanding is ground and neutral can be the same in the main panel, but must be separated in a subpanel. What are the ramifications of the fact that the subpanel is not wired correctly? Should it be rewired. It's an...

Isolating ground and neutral in a subpanel [ 1 Answers ]

Why do I need to isolate the ground and neutral in a subpanel when it is already bonded back at the main panel?

Subpanel Neutral & Ground On Same Bar [ 3 Answers ]

I just met with an electrician. I want to install a dedicated circuit in a sub panel. Since I live in an old multi-unit, the sub panel only has a neutral bar. I ask the electrician what are you going to do with the ground wire? The electrician replied, "Since the neutral bar is bonded, you can...

Connecting Ground bar and neutral bar [ 6 Answers ]

I'm wiring an additional panel into a garage. It's connected to the Meter through a switch that switches the power between the company power and a generator. The main house panel is inside the house. I understand that the neutral and ground are connected in the "main panel" only and any subpanel...

Subpanel Grounding Rods and Neutral Bar [ 7 Answers ]

My main service panel is installed in a detached garage. Our new home is fed by a subpanel run underground from the garage. At the garage panel I have two ground rods and the neutral bar and ground bar in the panel are connected. At the house subpanel location do I need additional ground rods...


View more questions Search