    Will aluminum #2 wire work with a 120 amp circuit breaker?
    Will aluminum #2 wire work with a 120 amp circuit breaker?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 10, 2011, 11:34 AM
    First off, assuming this in USA, 120 amp is not a standard overcurrent rating device setting.

    Second, to determine the amperage rating of a conductor, need to know the insulation type.

    I am sure there are other issues and question, let's go with the two I mention and we can go from there.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Aug 10, 2011, 05:15 PM
    Yes it will "work" but is not rated for 120 AMPS. Aluminum #2, 90 degreeC, as service feeder is rated at 100 Amps
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Aug 10, 2011, 06:54 PM
    Quote Originally Posted by ma0641 View Post
    Aluminum #2, 90 degreeC, as service feeder is rated at 100 Amps
    We would never use the 90 deg C column in figuring real circuit amps, but regardless of temperature, #2AL is rated for a 100A dwelling service.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Aug 11, 2011, 02:50 AM
    Novices reading the Code can be dangerous.

    The 90 degree C column of Table 310.16 is off limits to anyone that has not been trained to use the Code.

    This rating is only allowed to be used to rate ampacity if wire when the terminations are rated 90 degree C.

    This rating of terminals and connections is very rare. Only seen in high usage and industrial equipment, and usually special order.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire gauge for 35 AMP circuit breaker [ 3 Answers ]

What wire do you need to run from a 35 amp breaker. The application is for an air conditioner.

15 amp circuit breaker on 10 gauge wire [ 6 Answers ]

I want to run an outside light and receptacle about 250 feet from the main panel load center. It I use a 15 amp circuit breaker, is 10 gauge wire large enough?

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

Wire Size for 250 Amp breaker 3 phase 208Y/120 [ 1 Answers ]

Wire Size for 250 Amp breaker 3 phase 208Y/120


View more questions Search