    Will aluminum #2 wire work with a 120 amp circuit breaker?
    Will aluminum #2 wire work with a 120 amp circuit breaker?
  • Aug 10, 2011, 11:34 AM
    tkrussell
    First off, assuming this in USA, 120 amp is not a standard overcurrent rating device setting.

    Second, to determine the amperage rating of a conductor, need to know the insulation type.

    I am sure there are other issues and question, let's go with the two I mention and we can go from there.
  • Aug 10, 2011, 05:15 PM
    ma0641
    Yes it will "work" but is not rated for 120 AMPS. Aluminum #2, 90 degreeC, as service feeder is rated at 100 Amps
  • Aug 10, 2011, 06:54 PM
    stanfortyman
    Quote:

    Originally Posted by ma0641 View Post
    Aluminum #2, 90 degreeC, as service feeder is rated at 100 Amps

    We would never use the 90 deg C column in figuring real circuit amps, but regardless of temperature, #2AL is rated for a 100A dwelling service.
  • Aug 11, 2011, 02:50 AM
    tkrussell
    Novices reading the Code can be dangerous.

    The 90 degree C column of Table 310.16 is off limits to anyone that has not been trained to use the Code.

    This rating is only allowed to be used to rate ampacity if wire when the terminations are rated 90 degree C.

    This rating of terminals and connections is very rare. Only seen in high usage and industrial equipment, and usually special order.