    I need to run 220 amp service to an airconditioner will 6 gauge wire handle 40 amps?
    I need to run 220 amp service to an airconditioner will 6 gauge wire handle 40 amps?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jul 28, 2011, 04:20 PM

    Yes, it'll handle more than 40 amps.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jul 29, 2011, 03:07 AM

    I truly hope you mean that you have to run 240 Volts and not 220 amps!

    Table 310.16 gives you the size and amperage for listed wires and the max amperage for each wire.

    I will guess that the connections inside of the A/C equipment are listed at 75(C) and therefore we can use the center column of the "Copper" wires.

    A #8 AWG wire can handle 50 Amps using listed 75(C) connections.

    A #6 AWG wire can handle up to 65 Amps when used in a piece of equipment where the connections are listed at 75(C).

    If you have to use the 60(C) column, then a #8 AWG will get you a max of 40 amps and a #6 AWG will get you 55 Amps.

    If you truly mean that you need 220 amps then you will need wires that are 300 kcmil for 60 (C) for 240 Amp or 4/0 AWG for 230 Amp using 75(C).
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jul 29, 2011, 03:10 AM
    Quote Originally Posted by donf View Post

    A #8 AWG wire can handle 50 Amps using listed 75(C) connections.
    Don't forget, NM cable is limited to the 60 deg C column, so #8 is good for only 40A.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Jul 29, 2011, 03:24 AM

    Hey, Stan,

    Good morning! Care to join me for a metaphorical cup of coffee this fine day? I find out if I need shoulder surgery later today. Because of lung problems I'm a very high risk patient.

    On the brighter side, next week I find out if the Thyroid lumps are benign. I choose not to worry about the other possibility because my shoulder hurts a bunch and I'm real cranky, even with the "Oxy" pain killer pills, which don't seem to help all that much.

    Any way, here's mud in your eye!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire service, wire gauge 100 amp [ 9 Answers ]

I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...

Can a 20 amp fuse be use on 14 gauge knob & tube wire for airconditioner? [ 5 Answers ]

Can a 20 amp fuse be use on 14 gauge knob & tube wire for air conditioner? The 15 amp fuse breaker pops after use for an hour or two?

How far can I run 240v 30 amps in a 10 gauge or 8 gauge line? [ 4 Answers ]

I'm supplying electric to a remote building with no other power source. The generator supplies 240v 30 amp. How far away can I keep the generator outside with a 10 gauge line connecting to a service panel? What if I use 8 gauge? The building is used infrequently and I run an air compressor a few...

Wire sizing for 200 amp service with 220 ft. Run. [ 1 Answers ]

I built a new shop, pole building and need to run electric service to the shop. The pole with the transformer and ct meter that I will share with my residence is 190 ft. from shop. Total length of cable from transformer to sercice panel will be 218 ft. I will run this underground in appropriate...

What wire gauge for 400 amp service, 320 ft run? [ 7 Answers ]

Built a pole barn in the back yard, was going to upgrade the house service and run from there, but thanks to the county I am running separate service. I have the 3" conduit, I know I need to leave 35' coiled at the bottom of the utility pole, and want to run about 5' inside the barn to get to...


View more questions Search