Ask Experts Questions for FREE Help !
Ask
    DALewis's Avatar
    DALewis Posts: 1, Reputation: 1
    New Member
     
    #1

    Jul 19, 2011, 06:58 AM
    12 & 14 gauge wire on 30 AMP circuit
    I have a 30 AMP breaker and circuit feeding 10 gauge wire to several 15 AMP outlets. However, some of these outlets also have 12 and 14 gauge wire feeding off them to other outlets, light fixtures and switches. Doesn't this present a possible fire/short circuit hazard if one of the 12/14 gauge wires becomes overloaded?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 19, 2011, 07:01 AM
    Sure does present a fire hazard.

    With the #14 wire in the circuit, the breaker needs to be a 15 amp.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jul 21, 2011, 12:51 PM

    Also, understand that you CANNOT feed standard 15 or 20A receptacles from a 30A circuit, even if it is wired with all #10.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What gauge wire used for 20 amp circuit [ 3 Answers ]

15 amp draw on air compressor on start up runs at 8 amps on trips breaker while there is pressure in tank do I need to up my service from 15a to 20 a or do I have to do both 12/3wire or stay with 14/3 wire

Wire gauge for 35 AMP circuit breaker [ 3 Answers ]

What wire do you need to run from a 35 amp breaker. The application is for an air conditioner.

15 amp circuit breaker on 10 gauge wire [ 6 Answers ]

I want to run an outside light and receptacle about 250 feet from the main panel load center. It I use a 15 amp circuit breaker, is 10 gauge wire large enough?

Can you put in 15 amp outlets with 12 gauge wire on a 20 amp circuit [ 1 Answers ]

Can you put in 15 amp outlets with 12 gauge wire on a 20 amp circuit these are just regular household outlets not used for dryers or refrigerator. Or should I replace with 20 amp outlets