    Lost Water supply ground, How do I fix this ?
    My 200 Amp service was bonded by two driven rods and connection to my copper piping. I bought this house used and without much history. At some point it seems like the Water company changed the main line to a poly 3/4" line that hooks to my existing copper piping. Now all the copper pipe in my house is no longer grounded by the supply pipe. What should be done ? Should I drive another rod where the ground hooked up to my piping and connect there ? I am working in a crawl space, driving a rod would be tough. If I don't need to do a new rod should I disconnect the ground from my copper piping ? Thanks for your help
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 3, 2011, 03:05 AM
    I suspect you will not need to do anything.

    Confirm that there is a min of #6 copper wire connecting the neutral/ground bar in the panel with the Main Breaker to the two ground rods, and a min #8 copper wire from the neutral/ground bar to the copper cold water pipe in the home.

    The two ground rods ground the neutral/equipment ground of the electrical system, and the wire to the copper water pipe bonds the water pipe to equipment ground.

    Do not disconnect the wire bonding the water pipe.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jul 3, 2011, 06:16 AM
    Quote Originally Posted by tkrussell View Post
    ..., and a min #8 copper wire from the neutral/ground bar to the copper cold water pipe in the home.
    I know you know this, and I suspect it was just a typo, but this needs to be a #4cu, not #8. sized for the 200A service.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jul 4, 2011, 04:27 AM
    I hate when I do that, zoned out and forgot the 200 amp was posted had 100 Amp in mind.

    It needs to be a #4 copper.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Clog in water supply lines after replacing section at main municipal supply... [ 1 Answers ]

I had an exposed water supply line that ran from the city inlet to my house. It was old and rusty so we decided to replace it with a PEX pvc piping. It's the same dia. (3/4") and we replace the one 90 elbow with a 45 instead. When we turned the water back on, it had no pressure, and after my...

Sub panel supply and ground [ 1 Answers ]

I want to use a #6 aluminum 3 wire cable (2 conductors sheilded and one bare) that was used to feed a 50 amp oven to feed a sub panel that will supply a 40 amp circuit (20ft.) to a new oven ,1 20amp circuit dedicated to a micro wave, and 2 15 amp circuits to supply lighting (1000 watts per circuit)...

Supply line won't stop running. Main water supply off [ 3 Answers ]

I was doing some bathroom remodeling and attempted to remove an old supply valve. It would not budge so I decided to cut the copper tubing underneath it and put on a new shutoff valve with a compression fitting. The problem is that water just kept coming out of that supply line. The main water...


View more questions Search