    GFCI
    hello everyone,
    My GFCI continues to trip. I replaced it, same problem.I rewired with 12-2 for 20A breaker and GFCI. Itcan take over a day to rese without anything pluged in. Only one other receptacle is on this line. What I don't understand is that that load is 14-2 with 15A receptacle.(I did not wire that) I tried to isolate bot the pond pump plugged outside and the alarm system. Alarm only= trip, pond only= no trip. I also plugged the alarm by extension to a basement recpticle= no trip at the breaker. I was thinking that the pond pump might have a short but it has not tripped in 25 hours, the wire leading to the pump has not been rewired nor has the breaker been replaced. I was thinking of replacing the GFCI with a 20A receptacle and or disconnecting the load after the GFCI.all worked fine before the storm. I thought also that the Alarm may have shorted but it has not tripped the panel breaker as it had the GFCI.

    Any Ideas?

    Thanks----Don
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 8, 2011, 07:24 AM
    The problem may be a ground fault in the alarm system that the GFI device is sensing.

    Water may have entered the cable, or alarm.

    A standard breaker is not as sensitive as a GFI device, however you cannot leave it on a standard breaker.

    A GFI device will also trip due to length of wiring and not have any actual ground fault.

    Has this system worked fine for some time, or is this a new system?
    dcheffo's Avatar
    dcheffo Posts: 44, Reputation: 1
    Junior Member
     
    #3

    Jun 11, 2011, 09:49 AM
    Everything has worked for some time. It does not matter if the pond is plugged and/or alarm. The only thing left to replace is the breaker or the load wire all else is new. The breaker is now tripping with pump only. I'm thinking the problem might be the wire that is the load. How wolf I test the alarm for a fault?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gfci wiring and bathroom switch controlling the power on and off to gfci plug. [ 3 Answers ]

I got a concern caused by my brother in law, I have had to perform a bathroom reno and needed to upgrade the wall switches and install a gfci plug, well all wiring was OK till after the drywall went up and now, no power to vanity light(power is on wire as it goes through attic, nothing comes up at...

Can I put outside gfci, and laundry gfci outlets together on ciruit? [ 5 Answers ]

Hi, I am in the process of redoing my basement, adding a bathroom and laundry room. I would like to have one gfci protected outlet in the bathroom, one in the laundry room, and also add one outside (through the bathroom wall), I also would like a light in the shower stall which will need to be...

Changing 15 amp non-GFCI split to 20 Amp GFCI single (kitchen counters) [ 11 Answers ]

I have an older home and I am redoing the kitchen. The kitchen outlets are currently split ones as per the code of the day. They are presumably using 14 gauge wire. (or maybe it may be 12 since it is the 3 wire loomex) It is not practical to re-run the wire. One of them is quite close to a kitchen...

30amp GFCI to 50amp GFCI [ 1 Answers ]

I have a square D panel box with 200 amp service coming into the house. I have a square D 30 amp double pole gfci breaker that was put in last year for a hot tub. I am now getting a new hot tub, and it requires a 50amp gfci breaker. The 30amp currently in place says type/tipo HOM. It is...

When adding a GFCI disconnect for hottub, should I replace GFCI in service panel? [ 4 Answers ]

I have a hottub now but without a disconnect. Its simply a 6/3-50 amp wire that runs from the hottub to a 50amp GFCI inside the house main service panel. I want to install a disconnect 5-10 feet from the hottub. I bought a disconnect box that already has a GFCI inside of it. Should I have bought...


View more questions Search