    I am trying to wire a duplex receptacle with one half of the receptacle controlled by a switch (half-hot) and the other half by a GFCI.

    My approach is: 1) Break tabs on both sides of this receptacle. 2) using a 14/2 from Load side of GFCI to the bottom-half two screws of the receptacles 3) Using a 14/2 from a single pole switch to the top-half two screws of this same receptacle.

    Would that above approach work?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    May 10, 2011, 05:14 PM

    Only if the switch has power to it.
    thangrong's Avatar
    thangrong Posts: 4, Reputation: 1
    New Member
     
    #3

    May 10, 2011, 07:12 PM
    Power from 2 different branch circuits feed GFCI receptacle & switch separately. How to wire GFCI and switch from panel?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    May 11, 2011, 02:52 AM

    Are you asking how to wire two circuits to a split receptacle or are you asking how to wire a split receptacle after a GFI.

    Logic tells me that if one half of a receptacle needs to be GFI the other should be also.
    thangrong's Avatar
    thangrong Posts: 4, Reputation: 1
    New Member
     
    #5

    May 11, 2011, 06:02 AM

    I am looking to split receptacle half-hot controlled by a switch and the other half protected by GFI, which should be from a different circuit.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    May 11, 2011, 11:07 AM

    Well, it can be done, but why? The correct way would be to build a switch loop from the lower receptacle (hot) side to the switch with a return to the top brass screw.

    Normally, since this is a duplex receptacle you draw power from the constant on receptacle and feed the switch which in turn controls the top circuit.

    You accomplish this by breaking the brass side tab and leaving the silver tab connected.

    You would build the switch leg by connecting the white feed the switch from the pigtail for the lower receptacle. Connect the black from the switch to the brass screw on the receptacle top. Marker the re-tasked white with either black tape or magic marker at both the receptacle and the switch. At the switch, connect the white to the lower screw on the switch and the black to the upper screw on the switch
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #7

    May 12, 2011, 03:49 AM

    The method you originally described will work.

    Again I ask, if one half of the receptacle is GFI protected shouldn't the other half be also.

    Is there a real need for each half to be a separate circuit? If not wire as Don described.
    thangrong's Avatar
    thangrong Posts: 4, Reputation: 1
    New Member
     
    #8

    May 13, 2011, 12:16 AM

    The receptacle is currently protected by GFI. I want to create a switch to control the lamp in this room.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #9

    May 13, 2011, 05:23 AM

    Turn off power to circuit.

    Remove receptacle from box.

    Remove hot (black) wire from receptacle.

    Break tab between hot (brass) terminals of receptacle.

    Using a wire nut, connect hot (black) wire to white wire of cable going to switch and add a pigtail.

    Connect pigtail to one of the hot (brass) terminals of the receptacle.

    Connect black of cable going to switch to the other hot (brass) terminal.

    At the switch, connect the black and white wires to the switch terminals. It does not mater which wire connects to which terminal.
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

12 2 Wiring, a Wiring a 3 prong Dryer Receptacle [ 4 Answers ]

This cable has a white,and a black and a uncover coper wire. What order should these three wires be in, in a three prong receptacle?

Duplex wall switch wiring diagram [ 1 Answers ]

How do I wire a switch and a duplex outlet with only one wire from the box to the power source?

Wiring spst lighted rocker switches to split duplex receptacles [ 5 Answers ]

Hello, I am looking for help to wire some 16A spst lighted rocker switches to some split duplex receptacles so that each switch will control one outlet on each receptacle. I am doing this to create a panel which will allow me to turn on/off the equipment for my aquarium. This way I can choose...

Wiring GFI receptacle [ 2 Answers ]

Trying to wire a GFI receptacle at my kitchen sink. Receptacle in double gang box with a light switch. Original wiring consisted of two white wires to side of original receptacle. Two black wires to each terminal on the switch for a light over sink and a black jumper from switch to the...

Receptacle wiring [ 3 Answers ]

I want to add a receptacle to a box I have in my pantry that has an existing light switch. I have a three wire load coming in to the box from the circuit breaker. The red is wired to the switch and the blacks and whites are connected with wire nuts. The three wires feed other boxes in my kitchen....


View more questions Search