    220 Outlets & GFCI Questions
    I'm wanting to add some 220 outlets in the garage to run my woodworking equipment, and I have a couple of questions. First, can I run one 220 circuit with approximately 4 plugins on it? Only 1 piece of equipment will ever be used at one time (or does this violate code? ). Also, I'm under the assumption that since it's in a garage (attached) even the 220 circuits must be GFCI. Do I have to install GFCI breakers in my subpanel, or is there such a thing as a GFCI plugin for 220? Thanks for your help.
    Jim
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 6, 2007, 11:18 AM
    Sure, 4- 240 volt receptacles can be on one circuit.

    Code only requires 120 volt receptacles in a garage to be GFI protected.

    However, having a 240 volt circuit in a garage for the purpose of a power tool would be a good idea, and the only way to do this would be to use a 2 pole 240 volt GFI circuit breaker.
    JimV's Avatar
    JimV Posts: 5, Reputation: 1
    New Member
     
    #3

    Feb 7, 2007, 01:06 PM
    Thanks! Now if you could help me understand one other thing. I've looked over the three tools that will be run on the 240 volt circuit (again, only one at a time) and the one with the largest draw is the table saw (3hp, 220V, 18A). With that in mind how do I figure out the proper sized breaker and wire to complete this circuit? Thanks again.
    Jim
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Feb 8, 2007, 12:40 PM
    Branch circuit size is rated 125% of the running load of a motor, 18 x 1.25=22.5 amps, so the wire must be at least #10 with a 25 amp breaker. A 30 amp breaker is allowed also.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20 amp double pole gfci [ 9 Answers ]

I am working on an addition and am installing a whirlpool tub. The tub requires 2 - 20 amp GFCI protect circuits: 1 for the pump and 1 for the heater. I ran 12/3 wire in the walls thinking I could have the BLACK wire go from 1 GFCI breaker to the pump outlet and the RED wire go from a 2nd GFCI...

Can I use a 50 AMP GFCI where I once had a 60AMP? [ 2 Answers ]

I have a LA SPA Quest 8500 hot tub in my backyard (inherited from previous homeowner). It has a 60AMP GFCI box connected on the outside of the house which is then connected to a 60AMP breaker on the main in the basement. My 60 AMP GFCI oustide occasionally trips. I don't think there is anything...

Electric Thermostat 220 Volt 20 Amp [ 1 Answers ]

I am looking for an Electric Thermostat rated at 220vac @ 30 amps but can not find one. Does anyone know if they are available.

Outlets for GFI circuits - bath & kitchen [ 3 Answers ]

Hi - 2 questions: 1. I'm adding whirlpool bathtub as part of a remodel job. I've got 2 20amp dedicated lines, 1 for the pump, 1 for the heater. Each of these has to be on a GFCI breaker in the main panel, do I just use a regular receptacle under the tub enclosure, or is there a special...

GFCI & Switch [ 1 Answers ]

Can a GFCI be wired to run of a switch?


View more questions Search