    Can I run 8thhn from my service disconnect 100 ft to my shed sub-panel 6/12 box? Only asking because I really don't see the difference with what I was going to do, run 8thhn from my main circuit breaker box through two 50 amp cb's... across my garage... down my wall... buried in PVC under ground to the shed... connected to a sub-panel.

    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Apr 3, 2011, 08:06 AM

    NO, you cannot do this. Your service disconnect will not have the breaker space to install the sub-feed breaker. You CANNOT put the wires under the same lugs as the main feeder either.

    I hope you are describing all this that the WHOLE run is going to be in conduit. You cannot run THHN exposed at all.
    leureste's Avatar
    leureste Posts: 14, Reputation: 1
    New Member
     
    #3

    Apr 3, 2011, 10:14 AM
    Comment on stanfortyman's post
    Thanks, yes it will all be PVC'd
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Apr 5, 2011, 07:48 PM
    An 8 gauge wire can safely handle a 40 amp load. It MUST be fused / protected as such. If it were wired to the main feeder it would basically be unprotected which is not allowed for many reasons. 1, it's a fire hazard... 2, is't expressly forbidden by any electrical code... 3, it's plain *** stupid.
    leureste's Avatar
    leureste Posts: 14, Reputation: 1
    New Member
     
    #5

    Apr 5, 2011, 08:02 PM
    Comment on Missouri Bound's post
    Thanks, I already got pretty much the same answer already, going with original plan... route the wire from my main breaker box.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Apr 6, 2011, 02:40 AM
    Missouri, #8 THHN and THWN is rated 50 Amps. This includes pulled through conduit or if MC cable is used.

    #8 Romex or UF cable is rated 40 Amps.

    There does need to be a 2 pole 50 Amp breaker at the main panel to protect this circuit using #8 THHN/THWN pulled in PVC.

    If any section of the circuit is not THHN in conduit, say a section of Romex or UF, then it can only be rated 40 amps.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running wire behind basement wall [ 6 Answers ]

We have a basement with a finished wall. The finished wall is about 8" from the basement cement wall. So there's a "crawl" space all the way behind the wall. I want to fish/run a wire behind that wall. Speaking in terms of NEC Code, does the wire have to be fastened to the studs (which would be...

Running new wire behind plaster walls [ 4 Answers ]

If I run new wiring behind my plaster walls will there be any code issues because I am unable to tack it to a stud behind the plaster? I am trying to do this without destroying the walls.

Running wire through the wall [ 1 Answers ]

In my house, there's a gas fireplace that is housed in a 5'(W)x3'(D) wall enclosure. Poking into the enclosure, there's nothing around it. Just empty spaces. Now on the opposite side of that enclosure is the garage where the main circuit panel are found. I want to run some several wires...

Running THHN wire above 8 feet. [ 3 Answers ]

I am wiring a barn/shop area and have run all wiring in EMT conduit except above 8 feet where I have run some ROMEX to lights. My question is: I need one extra wire for a 3-way switch traveler wire. Can I staple this along side of the ROMEX wire above 8' in the hi bay area, or does it have to be in...

Running 14/2 wire [ 1 Answers ]

Hello, I will be running 14/2 wire with ground to run a wall a/c unit. The a/c unit pulls about 12.5 amps. Question is some part of the wire will be run outside under a deck. About 15 feet. This part I obviously will have to protect with conduit but is it really necessary for me to have to...


View more questions Search