    Neutral arced when cut
    I have 14-2 coming out of the panel in my garage with breaker on the black is hot tested it with tester that beeps faster if a wire is hot. I was cleaning up the end of the wires when I cut he end off the neutral with my side cutters the neutral arced is something wrong here or is it being energized from the neutal bar if so why does it not register hot when tested??
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 2, 2011, 06:46 AM
    If the breaker is on, the circuit is energized, and since the neutral is the return for the circuit, it would spark, since the circuit was interrupted.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Apr 2, 2011, 06:48 AM

    Any conductor when cut under a Load will arc.
    If you have 2 wire going to a light bulb(hot and neutral, and you cut the neutral, the power will go from the hot through the bul filiment and back to wher the neutral is cut, at the cut you would have no voltage from the panel, but would have voltage on the neutral from the bulb.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Apr 3, 2011, 08:12 AM
    Quote Originally Posted by tomjack View Post
    I have 14-2 coming out of the panel in my garage with breaker on the black is hot tested it with tester that beeps faster if a wire is hot. I was cleaning up the end of the wires when I cut he end off of the neutral with my side cutters the neutral arced is something wrong here or is it being energized from the neutal bar if so why does it not register hot when tested ???
    I bet this was a multi-wire circuit and the red was still live. This would potentially put the neutral under a load and do what you described.

    Two things. Do NOT rely on a proximity tester (the kind the beeps when near a live wire). They are unreliable for testing such as this.
    Also, in future replies and posts please try to write in sentences. It is extremely hard to decipher your posts the way they are written.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Do I just pull the main fuse to cut off power to the neutral bus bar? [ 9 Answers ]

I have an old "service protector (pellet)" attached to the bottom of my service panel. I believe it is the old school equivalent of a surge protector (My and GE's tech support's best guess). The two wires to the hot side are already disconnected, probably because it was only rated for 175 volts,...

Street lighting, neutral, cut [ 5 Answers ]

What does the underground neutral cable do in an aerial fed street lighting? What are the results of it being cut?

No power to electric outlet, after arced [ 15 Answers ]

I had an outlet in pantry, a pan slid down onto the outlet screw, it arced burning the pan and the screw, leaving the outlet useless, I tested the wires with testing light, showing no power. It is the only outlet not working, no breaker was thrown, what do you think the problem is?

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you

2000 mtd 42" cut rider will not go into neutral [ 5 Answers ]

when I went and picked this mower up (it had been sitting in a guy's backyard for 2-2 1/2 years), it went into neutral fine. We were able to push it onto the trailer with no problem. But, when I got to my house, and went to back the mower off the trailer, I could not get the thing to go into...


View more questions Search