    AFCI breaker keep tripping
    I have a new 20 Amp Afci breaker powering 7 outlets in a bedroom. (Unfinished basment). When I use my mitter saw, the breaker keeps tripping. When the saw is plugged into the exsisting 15amp gfci outlet, it works fine
    xracer's Avatar
    xracer Posts: 3, Reputation: 1
    New Member
     
    #2

    Mar 27, 2011, 05:45 PM
    Forgot to mention afci breaker is connected correctly. Return from outlets( white) is going to return/white terminal on the breaker. The white pigtail on the breaker is connected to the neutral bus in the panel. All grounds are connected.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Mar 28, 2011, 04:50 AM
    I suspect your miter saw motor uses brushes, which arcing produced at the brushes will be seen by the Arc Fault device as a problem.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Mar 28, 2011, 05:37 AM

    Do other things work in that outlet?
    xracer's Avatar
    xracer Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 28, 2011, 07:58 AM
    Other devices work OK on this circuit. Shop vac, elec drills, etc. I'll just have to use a different circuit to plug my saw into. Thanks for the replies..
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Mar 28, 2011, 08:03 AM
    These other itmes have motors that use brushes also, and make arcs.

    The AFCI breaker may be trying to tell you something is wrong with the miter saw.

    Or it may just not like it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trouble shooting an afci breaker [ 2 Answers ]

I have a bonus room we are trying to get permitted and the power is from a sub panel next to the room that fed a 220 volt circuit for a lathe in the garage and single 120v circuit. The light circuit was from the original wiring for the upstairs. The panel was fed with #8 three wire. The inspector...

A/C Breaker is tripping [ 2 Answers ]

I have an AC unit that I replaced the condenser fan in last year. This year during a storm the AC breaker on the inside of my house went bad. I replaced it and the AC worked fine for a few day. Last night I noticed the breaker had tripped. I reset the breaker and it runs for about 15-20 min. and...

I am having a problem with an AFCI circuit breaker tripping. [ 4 Answers ]

I have a circuit which, at this time, has just one duplex outlet. When I close the circuit breaker, it remains closed, when I plug a heater or a work light into the outlet the breaker trips. Are there any precautions to take on circuits fed by an AFCI circuit breaker? For example duplex outlets...

Why is my AFCI constantly tripping? [ 4 Answers ]

I have two bedrooms in my basement with two AFCI breakers (one for each br). One of the bedrooms keeps tripping. It seems like it is happening more and more frequently. I am afraid of a fire soon. Why is the breaker tripping? Should I just replace it or have the wiring looked at by an electrician?

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...


View more questions Search