    I am having a problem with an AFCI circuit breaker tripping.
    I have a circuit which, at this time, has just one duplex outlet. When I close the circuit breaker, it remains closed, when I plug a heater or a work light into the outlet the breaker trips. Are there any precautions to take on circuits fed by an AFCI circuit breaker? For example duplex outlets have two methods of making a connection - a push-in option and a screw down option. Should the push-in option be avoided? The heater and work light work fine on another circuit fed by a conventional 15 amp breaker.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    May 15, 2010, 09:27 AM
    It shouldn't trip with the work light, unless it is a type that uses an arc to strike... such as a high intensity lamp. The heater switch by design probably creates an arc when it goes on or off. And the screw down option is always preferred.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #3

    May 15, 2010, 02:47 PM

    The push hook ups use spring tension to hold wires. Over time the tension weakens from use because of heat from electric. This will cause outlet to stop working or will work intermittently.

    Try a regular light in outlet and see if it trips.

    Lets us know the outcome.

    Good luck

    Chuck
    RGPATTER's Avatar
    RGPATTER Posts: 26, Reputation: 1
    New Member
     
    #4

    May 18, 2010, 06:46 AM

    I think I have the answer. The AFCI breaker has two terminals - one for the hot supply wire and one for the return wire. The return wire must be connected to the neutral terminal on the breaker - not to the neutral bus. The white pigtail on the breaker is connected to the neutral bus. I had everything as it should be except I had the return wire going to the neutral bus.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #5

    May 18, 2010, 10:55 AM

    Glad u have solved problem. And welcome aboard.

    Chuck

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why is my circuit breaker tripping [ 2 Answers ]

Why is my breaker tripping

Circuit breaker keeps tripping [ 5 Answers ]

I just bought a new townhouse, but one month coming in, I have trouble with my distribution board... one of the circuit breakers 15amp, keeps tripping of late and is affecting my lighting and sockets which I find strange because it seems to me that those two ought to be separate. Could their be an...

A/C Circuit Breaker Tripping [ 3 Answers ]

Our A/C circuit breaker started tripping as the weather got hotter. It got to the point where it would trip after the A/C being on for less than a minute. I reset all the breakers, pulled the filters out of the vents and it continued to trip. The breaker would be very hot when I would check on it....

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Circuit breaker keep tripping [ 4 Answers ]

Hi, The problem is that the breaker trips and I cannot reset it, but after a few hours sometimes I can reset it but then it will trip again then when I try to reset it the breaker arc and woun't reset. Help!!


View more questions Search