    If I need conduit for this electric project, what size do I need?
    I am installing a hot tub outdoors. It requires 220-240 volt service. My main is 200amps. I have plenty of room to physically add the 50-amp double-pole gfci breaker that I'm going to use to feed a 50-amp gfci disconnect at the outdoor spa location. The panel is located within 30 wire-feet of the spa location. The spa is being installed on an elevated wood deck 15 feet off the ground. The panel is just inside the wall nearest the spa location. I'm planning on routing the cable through the wall, along the underside of the deck and terminating in the disconnect mounted to one of the 8x8 deck support posts. The cable I selected is Cerrowire 250 ft. 6/3 UF-B Wire Model # 138-4203T.

    Do I need conduit for this installation, or can I staple the cable to the deck joists?

    If I need conduit, what diameter do I need without violating conduit fill rules?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Mar 26, 2011, 04:46 PM

    I would use 3/4" PVC, 2 #6's for the hots,an 8 for the neutral, and a #10 for ground.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Mar 27, 2011, 04:15 AM
    You do not need a GFI breaker in the panel and at the tub. You can use a standard breaker in the panel, and the GFI at the tub.

    UF cable is acceptable since you are not burying it. It will be exposed underneath the deck, and your plan to staple it underneath is fine.

    If the cable is exposed top physical damage, for example, where it may rise through the deck floor up to the disconnect, it should be sleeved with conduit at that point.
    s_malt's Avatar
    s_malt Posts: 2, Reputation: 1
    New Member
     
    #4

    Mar 28, 2011, 06:11 AM
    Thank you for the replies. I used Stratmando's suggestion of using individual conductors (Southwire rated for indooor/outdoor applications) instead of the UF-B cable - savings of about $20. I also used the 3/4" conduit, but opted for the more expensive flexible LiquidTite to ease the conduit installation. I used tkrussell's suggestion to eliminate the GFCI at the main panel and saved $80 on that alone. Other than needing to paint the overly-obvious gray box mounted on my deck, I'm very pleased with the final installation.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

What size conduit? [ 1 Answers ]

Hello. I've already run underground about 50' of 3/4" conduit but have to pull out existing cable and replace with new cable. New cables will be: three #6 cables, one #8 and four #12's. I know it can be fished through but not sure if its code acceptable. I expect to upgrade my service panel some...

Conduit size [ 3 Answers ]

What is the minimum diameter grey pvc pipe for the following direct burial cable? Aluminum 4/0 2/0 4/0 urd? Aluminum 1/0 2/0 1/0 urd? Can I run a #4 copper ground wire in the conduit with the urd cables Thanks

How to size Conduit 6-3 [ 4 Answers ]

I have 2 6-3 for a 60ft run and 1 6-3 for another run. Question, what size conduit do I use. This circuit is for a tankless water heater. All will in my garage which is drywalled.


View more questions Search