    Conduit size
    What is the minimum diameter grey pvc pipe for the following direct burial cable?
    Aluminum 4/0 2/0 4/0 urd?
    Aluminum 1/0 2/0 1/0 urd?

    Can I run a #4 copper ground wire in the conduit with the urd cables

    Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 29, 2008, 10:46 AM
    Quote Originally Posted by kramwallace
    what is the minimum diameter grey pvc pipe for the following direct burial cable?
    aluminum 4/0 2/0 4/0 urd? Use 2" minimum
    aluminum 1/0 2/0 1/0 urd? Use 1.5" minimum (can I assume the 2/0 was a typo in this line?)

    can i run a #4 copper ground wire in the conduit with the urd cables Yes

    thanks
    ......................
    kramwallace's Avatar
    kramwallace Posts: 9, Reputation: 1
    New Member
     
    #3

    Aug 29, 2008, 10:55 AM
    stanfortyman

    Thanks for the response,
    I did type the second wire wrong, it is 1/0 2 1/0, will this handle a 100 amp panel
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Aug 29, 2008, 11:05 AM
    Yes it will.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size metal conduit should I use? [ 2 Answers ]

I have a cable 1.1 Inches in diameter. The National Electric Code says that a metal conduit cannot be filled more than 60%. It must have 40% of its space free. What size conduit should I use?

Wire & underground conduit size [ 1 Answers ]

Hi, I will need an electrical wire run between a small transformer and the main control panel for the house. I expect the transformer to push 220 or 240 volts at 200 amps. The transformer will be just under 140 feet from the panel. What size wire should I use and what is the minimum size...

How to size Conduit 6-3 [ 4 Answers ]

I have 2 6-3 for a 60ft run and 1 6-3 for another run. Question, what size conduit do I use. This circuit is for a tankless water heater. All will in my garage which is drywalled.

Proper wire and conduit size? [ 2 Answers ]

Hi, I have just had a new pole building built. I had a 200 amp service installed. I will be installing 16 fluorescent light units. I will install them on at least 2, possibly 3 circuits. My question is what is the formula for figuring out the proper wire size, and how many of these conductors can I...


View more questions Search