    My ongoing project;

    Small subpanel in attached garage- feeders will be #6 THHN copper and eqpt. Gnd. #10 THHN copper. Per Table C.1, 3/4" EMT will take four #6 THHN. The run will have two 90 degree bends and a total length of approximatley 23 ft.

    From and "ease of pull" standpoint will I have any trouble with the 3/4", or should I move up to the 1" EMT? Thanks
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Feb 27, 2011, 04:48 PM

    3/4" maybe fine, and depending on the Load, you might be able to Safely get away with 2 #6's, and 2 #10's(1 Neutral and 1 ground)
    afscme's Avatar
    afscme Posts: 23, Reputation: 4
    New Member
     
    #3

    Feb 27, 2011, 06:48 PM
    Strat,

    I was thinking that also, the load in general won't be great, lights and some power tools, but I will have a true 5HP compressor on the set up, so I'm not really keen on using a reduced neutral.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Minimum distance between emt conduit for data and emt conduit for power [ 1 Answers ]

Minimum distance between emt conduit for data and emt conduit for power?

EMT conduit [ 7 Answers ]

Hi again guys! I'm running about 8 feet of metal EMT conduit from a baseboard heater, into a junction box in the joist cavities of my basement (ceiling, or first floor joist cavity). The baseboard is 2000 watt, 240 volt, and my code here stipulates that 14/2 will suffice with 15 amp breaker. I'm...

EMT sizing [ 5 Answers ]

Question concerning the use of 1” or 1 ¼” EMT. I’ve referenced the NEC tables for conduit fill, but I’m concerned about the ease of the wire pull, and the amp/derating factor, which I am not that familiar with, or if it even applies. Local code requires conduit. This is the set up: 1. Apprx. 11...

Wires in emt [ 2 Answers ]

How many #12 wires in 1/2and3/4 metal tubing emt.allowed.

Rigid or EMT [ 2 Answers ]

Planning some remodeling. Main breaker panel, currently within five feet of the meter, may be moved approximately 12 feet due to the size of the panel and framing considerations. A listed service disconnect will be placed at the old panel location, and rigid used from meter to disconnect. ...


View more questions Search