    8 or 10 gauge wire for an appliance that draws 33 amps
    I'm setting a home brewery in the basement of my house. It's built around a piece of the commercial restaurant equipment that draws 33 amps. It's not a motor, it has a 9kW element so I'm was planning to use a 40 amp breaker (which I have room for) and 8 gauge cable but I've think I've read too much today and become confused. Do I need 8 gauge or is 10 OK.

    Thanks in advance
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 30, 2011, 05:00 AM
    You will not like the answer I give you, a 33 amp load needs a 50 amp breaker.

    Can use #8 copper if part of an MC cable . Or will need #6 copper NM Romex cable.

    Per the Code, electric heat circuit must be rated 125% of the load amps, 33 x 1.25 = 41.25 amps.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 30, 2011, 05:13 AM

    Besides, 9kW is 37.50A @ 240V, plus any motors, lights or controls.
    50A circuit it is!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 30, 2011, 05:25 AM
    Shows what happens when I take someone words. I did not check the 9 KW load amps.
    pkhop's Avatar
    pkhop Posts: 2, Reputation: 1
    New Member
     
    #5

    Jan 30, 2011, 12:48 PM
    Ouch, that's going to be expensive - It's a 50' run. The element is rated 9 kW at 230V. Thanks to both of you.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

How far can I run 240v 30 amps in a 10 gauge or 8 gauge line? [ 4 Answers ]

I'm supplying electric to a remote building with no other power source. The generator supplies 240v 30 amp. How far away can I keep the generator outside with a 10 gauge line connecting to a service panel? What if I use 8 gauge? The building is used infrequently and I run an air compressor a few...

HEATER draws 26 amps on the neutral wire [ 11 Answers ]

Hello, I just installed a 10 KW 240 volt heater in my garage. I used 4 GA wire and a 60 Amp breaker. Everything seems to work fine. However when I checked the current draw with my clamp-on ammeter, I see 41.7 amps on each hot wire and 26 amps on my neutral/ground wire. How can that be? I expected...

12 gauge wire @ 160 ft with 120 v and 14 amps will it work [ 1 Answers ]

Need to know if the amperage will be enough when it gets to the pump off a 20 amp breaker

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...


View more questions Search