    Hi,

    I am getting ready to finish my basement but my main panel is in my garage so I'm thinking it would make it easier for me if I install a subpanel in my basement. The main panel is 200 amp so I'd like to install a 100 amp subpanel. Is it okay to put in a 100 amp main breaker panel and feed it with a 100 amp double pole breaker from the main in the garage or should I get a main lug panel? Also I've been getting different opinions on the wire that needs to be run. Should I use #3 or #4? The run will be approximately 75 feet. So what type of cable should I ask for at the electric supply store? Thank you!
    TK_STL's Avatar
    TK_STL Posts: 4, Reputation: 1
    New Member
     
    #2

    Jan 27, 2007, 09:13 AM
    I probably should have mentioned that the basement will contain a bar area with at minimum a refrigerator and dishwasher. A bathroom, a theatre area with a lot of electronic equipment and someday maybe a hot tub. Also lots of lighting.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 27, 2007, 11:16 AM
    The wire can be a minimum #4 copper or a #2 aluminum. I would use a #2 - 4 aluminum wire SER cable. Will need to treat the connections properly with wire brushing, antioxidant compound and proper torquing. This cable is popular and readily available, and the least expensive.Will also need two 1" two screw squeeze connectors, one for each end of the cable. The cable will need to be protected if exposed to physical damage, or if passing through wood fraaming can use protection plates.

    Not sure what type of #4 cable would be available, most likely MC cable, with metal sheathing, and copper is very expensive now.

    The subpanel can have a main breaker , but does not need one. The subpanel will need a separate equipment ground bar for any and all ground wires from the branch circuit cables. The bare ground in the SER cable will connect to this also. This will leave the neutral bar in the subpanel isolated and just for neutral wires.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

60 AMP Subpanel Help [ 6 Answers ]

I would like to install a 60 amp subpanel. I plan to have a 60amp breaker in my main panel fed to a main lug subpanel. Questions: Can I use 6/3 Romex NM - the distance is about 65 feet? Can I use a 100amp main lug sub panel even though the main breaker is 60amps? I need four spaces in the...

Electrical Subpanel [ 1 Answers ]

I want to install a electrical subpanel(~50 amp) in my garage, if I do not feed the subpanel with a breaker from the main service of the house,would or could I tie into the main lugs of the main service to feed the subpanel? (Using the proper wire size) Would I have to use a ground rod for the...

Installing a Subpanel [ 3 Answers ]

I'm setting up a woodshop in my garage and want to install a subpanel to run my equipment off (it's going to be right next to the main). I'm starting from scratch, knowing extremely little about how to accomplish this. What sort of box do I need to buy, how do I size the breaker that will feed...

Grounding a subpanel [ 1 Answers ]

I have a set of direct current solar panels mounted on a metal structure (carport). All the panels and the structure are grounded to a ground rod driven near one of the support posts. Can I use the same ground rod for the ground connection of an alternating current subpanel mounted on one of...

Adding subpanel [ 6 Answers ]

I have a 200A main panel in my garage and want to install a subpanel in my basement to feed 4 circuits (15 & 20 A). The best route I can find for the feeder wire is through the garage in conduit, then entering the basement through the concrete foundation. I have a couple of questions. 1. If I...


View more questions Search