    Can I put 3 single 500 mcm conductors in 3 in conduit 120/240V
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 31, 2010, 01:08 PM
    Generally speaking, yes. However there is more detail needed to be accurate.

    The type of insulation and type of conduit is needed.

    The voltage is irrelevant, but do need to know is there if there is only the 3- #500 MCM, or is there an equipment grounding conductor also.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Dec 31, 2010, 10:31 PM
    DEpending on the tpe of wire, yes. That being said may I ask what it is you are doing with only three wires?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jan 1, 2011, 06:29 AM

    Extension of this thread: https://www.askmehelpdesk.com/electr...vc-539293.html
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Jan 1, 2011, 06:58 AM

    Could be a really long 120 Volt Line?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

240v transformer to 120,208,240v what wires [ 3 Answers ]

I'm replacing a 240v transformer in a split heat/cooling unit. The old trans has 4 prongs 2 load 2 line the new one has two secondary and 4 primary wires what wires do I use for primary?

What amperage is 5 sets of 500 MCM paralled good for? [ 5 Answers ]

5 Paralleled sets of 500 MCM, 3 Phase, what is the amperage rating good for?

Single Phase 120/240V I'm confused. [ 6 Answers ]

Okay so far in what I have learned I am still confused about this point. I understand the voltage is on a wave alternating to about +170V to -170V at 60 Hz meaning 60 times per second but averaging at + or -120V. How is it than that my single phase service can a give me 240V when I measure against...

500 & 600 MCM AL Wire Rating? [ 14 Answers ]

Could someone tell me how many amps 500 MCM AL and 600 MCM AL is rated for? Also, what size conduit do you think I'll need for 3 runs of 500 or 600? Never worked with or bought this size wire before, so trying to better prepare myself when going to pick up our materials. Thanks!


View more questions Search