    What amperage is 5 sets of 500 MCM paralled good for?
    5 Paralleled sets of 500 MCM, 3 Phase, what is the amperage rating good for?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 17, 2010, 09:03 AM

    If your pulling 5 sets of 500 MCM, you should be aware that the current rating will depend on the conductor material, insulation type, temp rating of terminations, quantity of current carrying conductors in raceway.

    If not, then you should not be pulling these conductors.
    dhsangree's Avatar
    dhsangree Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 17, 2010, 10:51 AM
    All that has been taken into consideration. The insulation being used is THHN, each set of 3 phases and 1 neutral are pulled in 5 - 4' conduits. Therefore, I still need the combined amperage rating of all these sets paralleled.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Dec 17, 2010, 11:31 AM

    OK, since you have taken all the specifc items I mentioned into consideration, and I still do not know all of them, all I can do is to suggest you must know what the amp rating of one set is, simply multiply by 5.

    All I know so far by your information is there are 4 conductors with THHN in each raceway.

    Copper or Aluminum?

    Terminations temperature rating?

    These two factors will dictate which column to use in Table 310.16.

    Typically, assuming copper wire, and 75 Deg C column, #500 MCM is rated 380 amps, times 5 sets will total 1900 amps.

    This assumes the neutral IS NOT current carrying. If the neutral will be for nonlinear loads, it will then need to be considered as current carrying, and the set of 4 conductors then need to be derated 80%.

    This still does not take into consideration any ambient temperature correction factors from the bottom of Table 310.16.

    So, as you can see, there are many factors to be determined to amperage rating of conductor, and with so little information given, I gave the answer of 1900 amps of what is a typical installation.

    Based on the variables to be concerned with, I may or may not be correct.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Dec 17, 2010, 12:53 PM
    Quote Originally Posted by dhsangree View Post
    All that has been taken into consideration. The insulation being used is THHN, each set of 3 phases and 1 neutral are pulled in 5 - 4' conduits. Therefore, I still need the combined amperage rating of all these sets paralleled.
    Anyone asking this should have the education/experience to not have to ask. Especially on a "Home & Garden" message board.

    What are you going to do with the information you get? Build the job? What if is it wrong, even by a little? What you are talking about is at minimum a mid 5-figure dollar job. Are you going to take a chance on a job like this?
    Even a small mistake could cost you $10's of thousands.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Dec 18, 2010, 07:39 AM

    Is this a homework question?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

A conductor that's described as a 750 MCM wire has an area of? [ 3 Answers ]

A conductor that's described as a 750 MCM wire has an area of?

Which is best among Internal 500 GB HD or External 500 GB HD [ 3 Answers ]

Hai, Just I proposed to buy one 500 GB Hard Dist for my Win XP/1GB RAM PC to store more data. Kindly clarify which is the best one Internal or External ? Tks Balakumar

500 & 600 MCM AL Wire Rating? [ 14 Answers ]

Could someone tell me how many amps 500 MCM AL and 600 MCM AL is rated for? Also, what size conduit do you think I'll need for 3 runs of 500 or 600? Never worked with or bought this size wire before, so trying to better prepare myself when going to pick up our materials. Thanks!


View more questions Search