New Member
|
|
Nov 22, 2010, 07:34 AM
|
|
Am I allowed to wire a 60a subpanel as 120v only?
Am I allowed to wire a 60a subpanel as 120v only? Two circuits, 15a and 20a will never need 240v. 40 feet from main panel use #6/2 AL? Can I add a ground bar to a Siemens EO2040ML1060 panel?
|
|
 |
Uber Member
|
|
Nov 22, 2010, 08:38 AM
|
|
A 120/240 volt panelboard cannot be used for 120 volt only.
A 120/240 volt systems must be at all panels, so #6-3 with ground cable will be needed.
Yes, a ground bar can be added to any panel.
|
|
 |
Uber Member
|
|
Nov 22, 2010, 03:46 PM
|
|
Look at the data plate on the box. It my say 120V 2 wire OR 240 Volt 3 wire. Just remember to identify the Neutral since a 6/2 will only have black feed lines. I'd also mark the box 120Volt only.
|
|
 |
Electrical & Lighting Expert
|
|
Nov 22, 2010, 03:50 PM
|
|
 Originally Posted by ma0641
Just remember to identify the Neutral since a 6/2 will only have black feed lines.
??
What kind of 6/2 are you buying?
|
|
 |
New Member
|
|
Nov 22, 2010, 04:47 PM
|
|
Comment on ma0641's post
It says 120/240v- 1 phase 3 wire and also 208/120v- 1 phase 3 wire. It has 2 connectors for hot independent of each other; does that mean I could use a 10/3 giving 30a to each terminal with a 15a off one and 20a off the other? What size ground?
|
|
 |
Uber Member
|
|
Nov 22, 2010, 07:20 PM
|
|
Comment on stanfortyman's post
My 70 year old brain was in a resting phase. I meant that in a 240 there is no neutral and SER has 2 black not 10/2
|
|
 |
Uber Member
|
|
Nov 22, 2010, 07:23 PM
|
|
Comment on ma0641's post
See TK's answer.
|
|
 |
New Member
|
|
Nov 23, 2010, 04:53 AM
|
|
Comment on stanfortyman's post
I already had the 6/2 NM left over and wanted to use it if I did not have to wire it 240. I know I would have had to label one wire as the neutral.
Thanks all, I'll buy 6/3 and go 240.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Wiring a 60A subpanel
[ 1 Answers ]
I am considering adding a 50A-60A sub-panel in my 6ft basement/crawlspace, to increase number of branch circuits I can run, and ease the running of some dedicated circuits. I am probably at least going to consult with a licensed electrician for this, if not having them install, but I like to have...
NEC compliant 120V subpanel connection?
[ 7 Answers ]
How many wires are needed for a 120V subpanel. I thought three is fine.. (Hot, Neutral, Ground) just the same as 4(Leg A, Leg B, Neutal, Ground) is fine with a 240V subpanel. 120V subpanels are very uncommon.. but I don't want or need 220v in this case. A Colorado inspector just dinged me for a...
Wire Size 60A Subpanel
[ 1 Answers ]
I am finishing up a bathroom addition and need to add a subpanel next to the existing 200A main panel to clean-up several 'doubled-up circuits I found in the main panel as well as provide breakers for the new bathroom installation.
I plan to install a 100A sub-panel within a foot of the...
View more questions
Search
|