    Am I allowed to wire a 60a subpanel as 120v only?
    Am I allowed to wire a 60a subpanel as 120v only? Two circuits, 15a and 20a will never need 240v. 40 feet from main panel use #6/2 AL? Can I add a ground bar to a Siemens EO2040ML1060 panel?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 22, 2010, 08:38 AM

    A 120/240 volt panelboard cannot be used for 120 volt only.

    A 120/240 volt systems must be at all panels, so #6-3 with ground cable will be needed.

    Yes, a ground bar can be added to any panel.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Nov 22, 2010, 03:46 PM
    Look at the data plate on the box. It my say 120V 2 wire OR 240 Volt 3 wire. Just remember to identify the Neutral since a 6/2 will only have black feed lines. I'd also mark the box 120Volt only.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Nov 22, 2010, 03:50 PM
    Quote Originally Posted by ma0641 View Post
    Just remember to identify the Neutral since a 6/2 will only have black feed lines.
    ??

    What kind of 6/2 are you buying?
    kkirkk's Avatar
    kkirkk Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 22, 2010, 04:47 PM
    Comment on ma0641's post
    It says 120/240v- 1 phase 3 wire and also 208/120v- 1 phase 3 wire. It has 2 connectors for hot independent of each other; does that mean I could use a 10/3 giving 30a to each terminal with a 15a off one and 20a off the other? What size ground?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #6

    Nov 22, 2010, 07:20 PM
    Comment on stanfortyman's post
    My 70 year old brain was in a resting phase. I meant that in a 240 there is no neutral and SER has 2 black not 10/2
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Nov 22, 2010, 07:23 PM
    Comment on ma0641's post
    See TK's answer.
    kkirkk's Avatar
    kkirkk Posts: 3, Reputation: 1
    New Member
     
    #8

    Nov 23, 2010, 04:53 AM
    Comment on stanfortyman's post
    I already had the 6/2 NM left over and wanted to use it if I did not have to wire it 240. I know I would have had to label one wire as the neutral.
    Thanks all, I'll buy 6/3 and go 240.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a 60A subpanel [ 1 Answers ]

I am considering adding a 50A-60A sub-panel in my 6ft basement/crawlspace, to increase number of branch circuits I can run, and ease the running of some dedicated circuits. I am probably at least going to consult with a licensed electrician for this, if not having them install, but I like to have...

Electrical subpanel fed from a subpanel: is this allowed? [ 1 Answers ]

Hello: Can I feed an electrical subpanel (or two) from a subpanel to the main? Thanks for your help!

NEC compliant 120V subpanel connection? [ 7 Answers ]

How many wires are needed for a 120V subpanel. I thought three is fine.. (Hot, Neutral, Ground) just the same as 4(Leg A, Leg B, Neutal, Ground) is fine with a 240V subpanel. 120V subpanels are very uncommon.. but I don't want or need 220v in this case. A Colorado inspector just dinged me for a...

Wire Size 60A Subpanel [ 1 Answers ]

I am finishing up a bathroom addition and need to add a subpanel next to the existing 200A main panel to clean-up several 'doubled-up circuits I found in the main panel as well as provide breakers for the new bathroom installation. I plan to install a 100A sub-panel within a foot of the...


View more questions Search