3-wire feed to subpanel in shed - bonding and grounding?
I have a 240 volt, 3-wire, 10 gauge feed from my house to a subpanel in a remote shed that has been there for at least 20 years. This feed is protected by a 30amp breaker on the house panel. There are no other metallic connections between the shed and the house The subpanel in the remote shed has one bus bar with the neutral connected to it. The neutrals and grounds of the circuits also connect into that bus bar. All of this is OK from what I can figure out (although not up to 2008 NEC). Here is where I am uncertain - the bonding strap from the bus bar to the panel case is not connected, and there is no grounding rod. Should the bus bar be bonded to the case and should I have a grounding rod with the wire connected to the single bus bar?
|
|
 |
Printers & Electronics Expert
|
|
Nov 15, 2010, 08:26 AM
|
|
Well you are correct that the installation does not meet current standards. 2008 Nec requires that Neutral and Ground can only be tied together at the main service panel or disconnect.
I believe that you current installation would be grandfathered and does not need to be changed. However, if you upgrade the sub-panel system, then the entire system would need to brought up to code.
Currently you need a four wire feed to the sub-panel. Ground and neutral would need to be isolated from each other at the sub-panel and you would need to put in a ground rod.
The ground rod is not for the electrical grounding of the system, the ground from the 4 wire feed back to the main panel would take care of that. It is there to protect against lightning.
|
|
 |
Ultra Member
|
|
Nov 15, 2010, 07:24 PM
|
|
You need to install a grounding rod at the shed. Pick up a separate grounding buss and have your grounds (if any) terminate there. The grounding rod will offer lightning protection, as donf said.
|
|
 |
New Member
|
|
Feb 18, 2011, 08:28 PM
|
|
If you plan on selling in the future, the home inspector(if thorough) might put it on the hit list to have another buss added to separate the ground wires from the neutral wires in the subpanel... So, if you feel like spending the money, it might save you time later to fix it now despite any grandfathering you're under at the moment.
|
|
 |
Uber Member
|
|
Feb 19, 2011, 04:49 AM
|
|
Since this installation was done before 2008, it can remain a 3 wire feeder. Any installation done before a Code edition does not need to be upgraded to meet any new Code.
Yes, connect the bonding jumper from the neutral bar to the panel's metal box, be sure that all neutral and equipment grounds are connected at the neutral bar.
Install a # 6 copper wire from the neutral bar to at least one 8 foot ground rod. Some states, that are sandy or rocky soil, such as Maine, require at least two ground rods for grounding.
If a home inspector in the future tells you to upgrade to a 4 wire system, tell him to go pound sand. You are perfectly within your legal rights to leave it as is.
The National Electric Code is NOT retroactive, and applies to NEW installations.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Service to a garden shed from a detached garage subpanel.
[ 3 Answers ]
Trying to find out if this possible and within code. I have a detached garage which has a 100 amp subpanel it it. 60 amps are being utilized by the garage, lights, receptacles, and at one time had a heater and 220v dryer connected. Dryer is gone and heater is too. I need to know if I can run a...
Grounding a subpanel
[ 0 Answers ]
I have installed a subpanel to supply electric power to my barn from a workshop. I used #2 aluminum underground wire which runs approximately 150 feet.
I have new breaker boxes at both ends of the service. I am feeding the subpanel through a 60 amp breaker at the shop.
The shop has an...
Grounding and bonding
[ 4 Answers ]
I am running electrical service from one building to another by running two hot wires, a neutral, and an insulated ground wire underground from from building #1 to building #2. Building #2 has a grounding system consisting of a piece of rebar labeled "electrical ground" protruding from the concrete...
Grounding rod for shed
[ 5 Answers ]
I have built a work shop in my back yard, I want to put a sub box in the shed.
The shed is 2 1/2 ft. from my main breaker box. I plan on putting a 100 amp
Breaker in the main box to feed the work shop sub box. The sub box will have
Separate c/b's for all the circuit's but no main breaker. My...
Adding a Subpanel to a shed
[ 7 Answers ]
I planning on adding a subpanel to my shed. I think I have done my homework and here is what I was planning. I was going to add double pole (40AMP 240 volt breaker) to my main panel. It is about an 80 foot run between my main panel and the subpanel I am adding. I already have schedule 80 PVC...
View more questions
Search
|