3-wire feed to subpanel in shed - bonding and grounding?
I have a 240 volt, 3-wire, 10 gauge feed from my house to a subpanel in a remote shed that has been there for at least 20 years. This feed is protected by a 30amp breaker on the house panel. There are no other metallic connections between the shed and the house The subpanel in the remote shed has one bus bar with the neutral connected to it. The neutrals and grounds of the circuits also connect into that bus bar. All of this is OK from what I can figure out (although not up to 2008 NEC). Here is where I am uncertain - the bonding strap from the bus bar to the panel case is not connected, and there is no grounding rod. Should the bus bar be bonded to the case and should I have a grounding rod with the wire connected to the single bus bar?