    12 awg thhn on 30 amp overcurrent
    Why can't you use a 30 amp overcurrent device on a 12 awg thhn conductor?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Nov 13, 2010, 06:15 PM

    12 ga. Wire should be protected by a 20 overcurrent device. First of all it's code (NEC). In addition to that, wire will overheat if exposed to heavy loads which can break down the insulation, melting it and exposing the wire in some situations. Obviously a bare wire is not safe in any respect when it is a current carrying conductor. It's simply not wise or allowed.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Nov 13, 2010, 06:35 PM
    Quote Originally Posted by ALJAMES View Post
    why can't you use a 30 amp overcurrent device on a 12 awg thhn conductor?
    You can, in very specific and rare instances, but that is not a topic for a DIY forum.
    NEC 240.4(G) is the code reference here.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 14, 2010, 04:35 AM
    Aljames, why do you ask?

    Stan is very correct, only in very specific and rare circumstances is it allowed, and I want to be sure this is understood.

    Generally speaking, and certainly in any DIY situation, the answer is no.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I use #6 AWG instead of #8 on 40 amp [ 4 Answers ]

I'm making a is a 40 foot run to a cooktop. It needs amps. #8 AWG is recommended but I don't have it on hand and want to use #6 instead. Sound OK?

Amp rating for 4 awg aluminum 600v [ 1 Answers ]

I am trying to find the max amp load for #4 AWG Aluminum 600v cable

Amp capacity for awg # 6 copper wire [ 1 Answers ]

I am replacing a standby generator. The wiring to the house is AWG #6 copper, THHN. The disconnects at both ends are 75 degree rated terminals. 240 1 phase What maximum size generator can I use ? Thanks

16 gauge AWG vs. 18 AWG - very important international lighting project [ 27 Answers ]

Hello! I have a wrought iron furniture and lighting design company based in Florence, Italy. We have a large project we're working on for the States, which includes several chandeliers, sconces and pendants. Our client has asked us to get in touch with their electrician, who will be installing...

Wiring different gauge wires (18 awg to 14 awg) [ 5 Answers ]

I recently bought a house that has a nice wall lamp in the living room that I would like to keep as I renovate it. The lamp came wired with 18 awg wire (1 neutral, 1 hot, and 1 ground). The previous owner wired the lamp to a standard wire with a plug to make it a plug-in fixture. I don't know if...


View more questions Search