    220v air compressor
    I want to hook up 220 in my garage for a air compressor I just bought, I've ran a 110 line to the garage before for a smaller air compressor, I have 200 amp service panel with plenty of open slots. The air comp has just 3 wires, red, black, and green. Do the breakers go in the same way as the 110v breakers? If somebody could give me the basics I'm sure I can do it,! THANKS, MARK
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Nov 12, 2010, 08:25 PM

    You will use a two pole breaker. The red and black will connect to the breaker, the green is your ground. Read the label on the motor to verify the amperage and choose the wire and breaker accordingly. The breaker goes in exactly like the 120v breakers, except that it takes up two slots in the panel.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Nov 13, 2010, 04:25 PM

    If you are in the U.S.A. the voltage is 240.

    Question,

    Should not the poster get the nameplate amperage off the motor plate and then get the "Full Load Current" out of the tables in Article 430, to correctly size the conductors and required breakers or is this overkill?
    fuseman's Avatar
    fuseman Posts: 11, Reputation: 4
    New Member
     
    #4

    Nov 13, 2010, 05:51 PM
    How many hp is the motor, and how far away will the compressor be from the power or socket.
    fuseman's Avatar
    fuseman Posts: 11, Reputation: 4
    New Member
     
    #5

    Nov 13, 2010, 05:54 PM
    What is the full load amps say on the lable of the motor.
    Camaro00440's Avatar
    Camaro00440 Posts: 8, Reputation: 1
    New Member
     
    #6

    Nov 13, 2010, 07:33 PM
    thanks guys... it's 6.5hp... 15amp... l.r amps = 93... output 298kw... this is what's on the motor
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #7

    Nov 13, 2010, 08:23 PM

    Use a 20 amp breaker for that... 12 ga. Wire.
    Camaro00440's Avatar
    Camaro00440 Posts: 8, Reputation: 1
    New Member
     
    #8

    Nov 14, 2010, 09:13 AM
    I bought 10gauge wire, the compressor is about 25 ft away from the breaker panel, and a 20amp breaker, is this OK? Over kill. Or not enough ? Going to put a plug on it because I want to plug in a 220 welder too!
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #9

    Nov 14, 2010, 12:39 PM

    It's absolutely fine. It will also allow you to move up to a 30 amp breaker should your needs change.
    fuseman's Avatar
    fuseman Posts: 11, Reputation: 4
    New Member
     
    #10

    Nov 15, 2010, 08:45 PM
    Hook the compressor up,and plug and wire 25' is long enough,let us know how its going.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #11

    Nov 15, 2010, 08:58 PM

    Now I'm confused. Are you running a circuit for the compressor using 10/3 wire, or are you putting a 10/3 wire on the compressor with a plug on the end of it? Not quite the same. Fuseman's last post has me wondering exactly what it is you are doing, and could definitely change the advice given.
    Camaro00440's Avatar
    Camaro00440 Posts: 8, Reputation: 1
    New Member
     
    #12

    Nov 16, 2010, 03:21 PM
    OK, I'm running 10/2 wire ( red, black, green) from the breaker panel, 25ft into the garage (attached) to a plug in the wall, then 10/2 wire from the compressor to the plug, about 5ft, (20amp breaker in the panel ) I'm using a plug so I can plug in a 220v wire welder also!! (when compressor's not plugged in)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My air conditioner compressor and outdoor fan does not turn on. No Cold air [ 4 Answers ]

I turn my central air conditioner on and I get nothing. Everything is dead. I finally realize that the 3 amp fuse was blown. I replaced the fuse and turn on the air and the fuse gets blown again. I replaced the fuse and this time I turn the heat on. Everything works great. Fuse did not get blown...

Central air cond air handler doesn't come on but compressor does. [ 98 Answers ]

If I don't turn the central air on in the morning, when the attic is cooler, the air handler won't come on but the compressor outside fires up. At night when the attic cools down, the air handler will work. I have replaced the T-Stat but that didn't help. Today, I put the fan on first, and it...

My ac compressor is throwing out cool air but the iunside air is not cold [ 0 Answers ]

The fan is running on the outside unit and the inside unit is not throwing cold air what could it be

Air handler works fine but compressor will not shut off. Air is cold. [ 1 Answers ]

I noticed the floor was very cold at the airhandler closet. A coils are clean in airhandler and I replaced the filter.My outside compressor just keeps running without stopping.Airhandler seems to be cycling on and off like it should.

Amana air conditioning compressor fan runs but compressor does not [ 9 Answers ]

I have an Amana Model RCE30A2B Compressor unit installed it is about 6 years old, the compressor will not cut in when demanded yet the cooling fan for the unit does


View more questions Search