  • Nov 12, 2010, 07:14 PM
    Camaro00440
    220v air compressor
    I want to hook up 220 in my garage for a air compressor I just bought, I've ran a 110 line to the garage before for a smaller air compressor, I have 200 amp service panel with plenty of open slots. The air comp has just 3 wires, red, black, and green. Do the breakers go in the same way as the 110v breakers? If somebody could give me the basics I'm sure I can do it,! THANKS, MARK
  • Nov 12, 2010, 08:25 PM
    Missouri Bound

    You will use a two pole breaker. The red and black will connect to the breaker, the green is your ground. Read the label on the motor to verify the amperage and choose the wire and breaker accordingly. The breaker goes in exactly like the 120v breakers, except that it takes up two slots in the panel.
  • Nov 13, 2010, 04:25 PM
    donf

    If you are in the U.S.A. the voltage is 240.

    Question,

    Should not the poster get the nameplate amperage off the motor plate and then get the "Full Load Current" out of the tables in Article 430, to correctly size the conductors and required breakers or is this overkill?
  • Nov 13, 2010, 05:51 PM
    fuseman
    How many hp is the motor, and how far away will the compressor be from the power or socket.
  • Nov 13, 2010, 05:54 PM
    fuseman
    What is the full load amps say on the lable of the motor.
  • Nov 13, 2010, 07:33 PM
    Camaro00440
    thanks guys... it's 6.5hp... 15amp... l.r amps = 93... output 298kw... this is what's on the motor
  • Nov 13, 2010, 08:23 PM
    Missouri Bound

    Use a 20 amp breaker for that... 12 ga. Wire.
  • Nov 14, 2010, 09:13 AM
    Camaro00440
    I bought 10gauge wire, the compressor is about 25 ft away from the breaker panel, and a 20amp breaker, is this OK? Over kill. Or not enough ? Going to put a plug on it because I want to plug in a 220 welder too!
  • Nov 14, 2010, 12:39 PM
    Missouri Bound

    It's absolutely fine. It will also allow you to move up to a 30 amp breaker should your needs change.
  • Nov 15, 2010, 08:45 PM
    fuseman
    Hook the compressor up,and plug and wire 25' is long enough,let us know how its going.
  • Nov 15, 2010, 08:58 PM
    Missouri Bound

    Now I'm confused. Are you running a circuit for the compressor using 10/3 wire, or are you putting a 10/3 wire on the compressor with a plug on the end of it? Not quite the same. Fuseman's last post has me wondering exactly what it is you are doing, and could definitely change the advice given.
  • Nov 16, 2010, 03:21 PM
    Camaro00440
    OK, I'm running 10/2 wire ( red, black, green) from the breaker panel, 25ft into the garage (attached) to a plug in the wall, then 10/2 wire from the compressor to the plug, about 5ft, (20amp breaker in the panel ) I'm using a plug so I can plug in a 220v wire welder also!! (when compressor's not plugged in)