    Proper ground for 1000 amp service
    Im running a 1000amp service using 3 runs of 500mcm in 3 runs each in 3-1/2 ridgit, what should I pull for a ground in each run?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 8, 2010, 02:21 PM
    You need each conduit to have a #2/0 copper or #4/0 aluminum, as per the National Electric Code 2008 edition:

    (F) Conductors in Parallel. Where conductors are run in parallel in multiple raceways or cables as permitted in 310.4, the equipment grounding conductors, where used,
    Shall be run in parallel in each raceway or cable. Each parallel equipment grounding conductor shall be sized on the basis of the ampere rating of the overcurrent
    Device protecting the circuit conductors in the raceway or cable in accordance with Table 250.122.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

How many 500mcm wires for a 1000 amp service [ 13 Answers ]

I have a upgrade from 600amp to 1000amp service there are 2 3" conduits from breaker up to weather heads I am pretty sure I need 3 sets of 500mcm per phase can I change the 3"conduits to 4" and split up the phases in that short distance.

200 amp service ground [ 5 Answers ]

I am replacing an old 200 amp meter base with a 200 amp meter base with a built in disconnect breaker. From here I will feed the 200 amp panel inside. My question is about the ground. I have PEX plumbing, but the supply to the house is galvanized. I understand I need to bond the water supply...


View more questions Search