    Amana Heat Turns ON/OFF Too Fast!
    Just recently my Amana GUCA/GCCA will turn the heat on for 4 minutes or so, turn off, flash 4 times (clean filter, blocker return grill) and then will restart. I did replace the filter but did not resolve the situation. I am guessing maybe Primary or Auxiliary Limit looking at the book. I had replaced the controller board last year and have check both pressure switches and they seemed fine. The flame looks good up to the time it quits. Not sure what to do for sure before I call somebody. Any help would be great since the house in getting cold!!
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Nov 7, 2010, 08:44 AM

    4 is high limit switch, could be getting week, or you could have too much gas pressure. Doe you have any damper? Or closed registars?
    cdesrosier's Avatar
    cdesrosier Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 7, 2010, 06:57 PM
    I do not have any closed registars and do not have any dampers. I did play with it a little bit tonight. At around 2 minutes and 30 seconds, the flame would go out. I measure the primary limit switch and it did seem to open up with my meter. I unplugged the 2 wires and shorten them together and the funance came back up and ran past the previous shut time until the room temperature was met. I am guessing that means it is the primary switch might have gotten weak. Would that be the high limit switch you are referring to? My air flow seems to be good. It is possible to have a different problem? Do you possibly have the part number I need to purchase? Any other things I should check next? Thanks for all of your advice so far!

    Chuck
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Nov 7, 2010, 07:19 PM

    Well if it is the high limit switch. Like I said sometimes the switch will just get weak. But you may have a more serious problem. If your filter is clean and you are getting good airflow. You may have to high of gas pressure. ( have you seen the gas company working anywhere near your house?) The may have messed with the gas pressure in your area. Or you could have a cracked heat exchanger causing the limit to trip. You may want to have it checked out. A good way to tell if it may be the heat exchanger is watch to see if the flames change any when the fan comes on, or go outside and sell the vent of the plastic pipe. If you have a real foul egg type smell it may be bad news. How old is the furnace?
    cdesrosier's Avatar
    cdesrosier Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 7, 2010, 07:39 PM
    I have not seen any gas work in my area to my knowledge. The flame seems pretty constant when looking at it. IT does have the nice blue burning flame. I haven't smelled the raw natural gas smell at all but I will need to get outside tomorrow and check it out. Would I also smell the gas in my house coming out of the registars? My gas fireplaces and water heaters have been doing fine. We had not been using the heat at all until recently and this problem creaped up so it seems like a new problem for cranking up the heat for another year. The Amana system is probably 8 years old. I don't believe the switch is that expensive. Would it be a bad idea to purchase one to see if that is the problem before I have anyone come check for a cracked exchanger?

    Thanks again,
    Chuck
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #6

    Nov 7, 2010, 07:47 PM

    I would say if you do not see a change in the flame. And the vent does not smell bad. Then change the limit switch. Probably about $28 take the old one with you. It will have the temp range on it. You should be able to pick one up at any hvac store
    forjerry's Avatar
    forjerry Posts: 5, Reputation: 1
    New Member
     
    #7

    Feb 8, 2011, 11:52 PM
    I cleaned my flame sensor with sand paper and my Amana AMV9 seems to be working fine. It was cycling on and off with NO blinking codes resulting. I plan to also purchase a new sensor to replace this one. Hope that helps...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

Amana 80 SSE Heating - works for 5 seconds then turns off [ 2 Answers ]

I have an Amana 80 SSE heater. I read through the site and found out that I had no blinking series of lights - everything seems fine. I took an air can and cleaned out the flame sensor and it worked fine for a few days but now it is back to the same old problem - turns on and lights up for 5...

My Amana Gas heater turns on and then after a short burst stops. [ 4 Answers ]

My Amana GUI*/GCI* gas fired warm air furnace located in the attic turns on and then after a short burst stops. Gas flames start and shut off after a few seconds. The fans do not have a chance to turn on to blow the heat.

Amana dryer-heat start then turns off [ 0 Answers ]

I have an Amanda Clothes dryer model NDG2330AWW. The heat turns on for about two minutes, then stops. The dryer continues to spin. The ignitor works. All vents are clear. Any suggestions?

Amana Gas Dryer won't heat on heat cycle [ 2 Answers ]

I have an Amana gas dryer about 10 years old. The dryer will heat and the timer will advance on the timer cycle but it will not heat on the heat/more heat cycle. I have cleaned the lint vent entirely. I can see the ignitor get red hot and then ignites the gas on the timed setting. I am not sure...


View more questions Search