    Can the 4AWG Bare Copper wire from my generator to Grounding Rod be exposed?
    I am installing a standby generator on a concrete slab and there is about 4.5 ft from the grounding rod to the connection on the generator. I am using bare 4AWG copper wire and a copper rod. I am going to bury the rod and clamp and just leave the 4.5ft length exposed. Is this OK? I have no way to bury the length. Should I use plastic conduit to cover this length?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 22, 2010, 02:33 AM
    The wire does not need conduit if you bury it.
    hollywub's Avatar
    hollywub Posts: 3, Reputation: 1
    New Member
     
    #3

    Oct 22, 2010, 09:26 AM
    Tkrussel. I can not bury it because the slab is already in place. So for the 4.5ft that is exposed I should use conduit?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 22, 2010, 09:41 AM
    OK, I misread your question.

    The #4 wire does not need conduit if it would not be subjected to physical damage.

    Use conduit to protect it, it it can be damaged.
    hollywub's Avatar
    hollywub Posts: 3, Reputation: 1
    New Member
     
    #5

    Oct 24, 2010, 08:09 PM
    Comment on tkrussell's post
    Thank you. All installed. Passed inspection.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why does my 8 3 wire with ground have a bare coper wire [ 7 Answers ]

I am installing a range with 8/3 with a ground it has a red-black for hot white for nutral, green for equipment ground bar and a bare copper wire ground. The receptical has red/black/green/white but no place for the bare wire to hook to. Should I cut this off or hook it to the green

Can a bare copper ground wire be exposed in wall? [ 7 Answers ]

I recently purchased a home with an outdoor shed. I've started to remodel the shed and I noticed that the sub-panel was wired incorrectly. Neutral and ground were attached to the same bus, and there was no ground rod. I've purchased a new bus bar for ground and I am in the process of installing my...

Bare copper wire; [ 3 Answers ]

Bare copper wire; Why do we use bare copper wire for grounding, why not all insulated?

Using the ground or (bare) wire for the neutral wire [ 2 Answers ]

I have a problem with some wiring that I ran for an outside motion light. Although the hot leg and ground wires are fine, the neutral wire is defective ( it may have gotten knicked or something). Of course, now the wiring is covered up behind a wall that I do not want to tear into if it can be...


View more questions Search