  • Oct 22, 2010, 01:46 AM
    hollywub
    Can the 4AWG Bare Copper wire from my generator to Grounding Rod be exposed?
    I am installing a standby generator on a concrete slab and there is about 4.5 ft from the grounding rod to the connection on the generator. I am using bare 4AWG copper wire and a copper rod. I am going to bury the rod and clamp and just leave the 4.5ft length exposed. Is this OK? I have no way to bury the length. Should I use plastic conduit to cover this length?
  • Oct 22, 2010, 02:33 AM
    tkrussell
    The wire does not need conduit if you bury it.
  • Oct 22, 2010, 09:26 AM
    hollywub
    Tkrussel. I can not bury it because the slab is already in place. So for the 4.5ft that is exposed I should use conduit?
  • Oct 22, 2010, 09:41 AM
    tkrussell
    OK, I misread your question.

    The #4 wire does not need conduit if it would not be subjected to physical damage.

    Use conduit to protect it, it it can be damaged.
  • Oct 24, 2010, 08:09 PM
    hollywub
    Comment on tkrussell's post
    Thank you. All installed. Passed inspection.