Ask Experts Questions for FREE Help !
Ask
    MikeSmith's Avatar
    MikeSmith Posts: 2, Reputation: 1
    New Member
     
    #1

    Oct 13, 2010, 11:05 AM
    Direct burial electrical wire?
    I would like to run a 50amp circuit or sub-panel 400 ft to a barn/pottery studio which could supply both 220 and 110v power, to be used to run lights, heat and kilns. What size direct burial wire would I need?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Oct 13, 2010, 06:42 PM
    That's a pretty long run... you would need #1 wire to minimize voltage drop at that distance. You will also need a ground wire... and a grounding rod at the location. How many circuits do you plan on running?
    MikeSmith's Avatar
    MikeSmith Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 14, 2010, 06:37 AM
    Comment on Missouri Bound's post
    I have a 50amp receptical box w 1-20amp breaker 240v and 1-10amp breaker 120v that should be more than sufficient for my needs, so just one circuit connecting that.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Oct 14, 2010, 12:11 PM

    Mike,

    What do you plan on using the 10 Amp breaker for?

    Also, I believe that you would need 1/0 AL to overcome the voltage drop caused by the distance.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Oct 14, 2010, 01:40 PM
    OK, so now there are two different answers to the posters question.

    Which is it, #1 or #1/0?

    Aluminum or copper?

    What amperage is being used to calculate voltage drop?

    What voltage?

    These voltage drop questions not only need accurate answers, but should contain the values used to calculate.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Oct 14, 2010, 02:29 PM

    This is for a pottery shed. I have done a LOT of wiring for pottery people. One thing I know is that they are never satisfied with their kilns. They tend to go bigger and bigger.

    To say you have a very remote (400' away) pottery shed that only needs a 50A feeder, for everything, makes me very skeptical.
    I have had to provide 100A circuits for kilns in a residence more than once.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #7

    Oct 14, 2010, 05:09 PM
    #1 copper, 50 amp, 240v
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Oct 14, 2010, 05:46 PM


    <Left out information>
    I chose AL because of the distance/cost. Using 60c UF cable, continious load I came up with 1/0 AL

    Also used 50 Amp 120/240. I calculated using the 120 to neutral and came up with the 1/0.

    And you get to pick the correct route taken.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size wire do I need to run to get a 100amps. 225ft. using direct burial wire? [ 5 Answers ]

What size wire do I need to run to get a 100amps. 225ft. using direct burial wire coming from a 200amp. Service? Any info. Would be appreciated. Regards, Garry

Direct burial electrical cable [ 10 Answers ]

I'm running power to a shed / barn. NOT in the city, so code is not a problem, but I DO have an NEC book. I need to go 300' -- and want to use best cost effective. 240v not needed, but I was considering 2/2/2 aluminum anyway. Question: Is SEU rated... or at least acceptable.. for direct...

14 gauge direct burial wire [ 1 Answers ]

I was wondering if I can use direct burial 14 gauge wire from my garage about 10 feet to a new gfci outlet which I will drill through the brick to be on the outside of the wall of the garage to the outside? The garage has no drywall just going to run it through the studs

Direct Burial Electrical Cable [ 1 Answers ]

I am planning on running an underground electrical cable to my garage. I plan on placing a 100 apm panel in the garage and run from my house main electrical feed. What kind of wire do I need to do the job?


View more questions Search