Doubling up wire
Wondered how the NEC feels about using parallel feeders instead of footing the cost for more expensive larger sized wire? Application is UF-B from house to detached garage. Want to use 2 sets 12-3, WG instead of paying for 10-3 WG (or 8-3 WG). Am not interested in having an inspection.
|
|
 |
Uber Member
|
|
Apr 12, 2005, 08:59 AM
|
|
I can't give you what code says. I do know it is quite common to use multiple wires to carry large industrial 3 phase loads. I have seen things like 3 conduits each carrying three 500 MCM singles. They are quite common in factories.
|
|
 |
Full Member
|
|
Apr 12, 2005, 09:35 AM
|
|
I guess...
 Originally Posted by labman
I can't give you what code says. I do know it is quite common to use multiple wires to carry large industrial 3 phase loads. I have seen things like 3 conduits each carrying three 500 MCM singles. They are quite common in factories.
... it would be a better bet to place them in PVC conduit so if they ever are found to violate code, they can be replaced easier. You agree, Labman?
|
|
 |
Uber Member
|
|
Apr 12, 2005, 11:54 AM
|
|
Certainly wouldn't hurt. Do you already have a big coil of 12-2? Again you buy 2 lengths of it plus the conduit, surely one length of 10-2 would be cheaper. Also if you run conduit, you could run singles rather than cable. Stranded singles pull easier than solid cable.
|
|
 |
Uber Member
|
|
Apr 13, 2005, 01:00 PM
|
|
Per the current edition of the National Electric Code:
"Section 310.4 Conductors in Parallel.
Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."
Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.
Something to consider.. save a few bucks now, and pay large bucks later.
|
|
 |
Full Member
|
|
Apr 13, 2005, 07:53 PM
|
|
Thanks for the...
 Originally Posted by tkrussell
Per the current edition of the National Electric Code:
"Section 310.4 Conductors in Parallel.
Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."
Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.
Something to consider..save a few bucks now, and pay large bucks later.
... info and the reminder of just how dangerous electricity is!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Neutral wire is hot(has voltage potential like the black wire)
[ 5 Answers ]
Hi,
The problem started at midnight last week. One of my line in the basement is starting to have issue whenever I connect a water pump or appliances to the outlets. Before I plug the appliance in, the neutral is neutral(zero voltage), but when I plug the appliance in, the neutral is now...
3-wire home, 3-wire fan, 2-wire remote
[ 9 Answers ]
Greetings,
My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use...
The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....
4 wire home service entrance wire size
[ 1 Answers ]
Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?
2 Wire White-Rogers with no wallplate wire question
[ 2 Answers ]
Hi there.
I want to replace my current White-Rogers 1E56W309 thermostat with a new Honeywell RTH7500D. The problem is that the tools that installed my high efficiency furnace didn't install the wall plate with my thermostat (it was a new house and the builder contracted these guys). Instead,...
View more questions
Search
|