Ask Experts Questions for FREE Help !
Ask
    Flickit's Avatar
    Flickit Posts: 278, Reputation: 2
    Full Member
     
    #1

    Apr 12, 2005, 07:37 AM
    Doubling up wire
    Wondered how the NEC feels about using parallel feeders instead of footing the cost for more expensive larger sized wire? Application is UF-B from house to detached garage. Want to use 2 sets 12-3, WG instead of paying for 10-3 WG (or 8-3 WG). Am not interested in having an inspection.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Apr 12, 2005, 08:59 AM
    I can't give you what code says. I do know it is quite common to use multiple wires to carry large industrial 3 phase loads. I have seen things like 3 conduits each carrying three 500 MCM singles. They are quite common in factories.
    Flickit's Avatar
    Flickit Posts: 278, Reputation: 2
    Full Member
     
    #3

    Apr 12, 2005, 09:35 AM
    I guess...
    Quote Originally Posted by labman
    I can't give you what code says. I do know it is quite common to use multiple wires to carry large industrial 3 phase loads. I have seen things like 3 conduits each carrying three 500 MCM singles. They are quite common in factories.
    ... it would be a better bet to place them in PVC conduit so if they ever are found to violate code, they can be replaced easier. You agree, Labman?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Apr 12, 2005, 11:54 AM
    Certainly wouldn't hurt. Do you already have a big coil of 12-2? Again you buy 2 lengths of it plus the conduit, surely one length of 10-2 would be cheaper. Also if you run conduit, you could run singles rather than cable. Stranded singles pull easier than solid cable.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Apr 13, 2005, 01:00 PM
    Per the current edition of the National Electric Code:

    "Section 310.4 Conductors in Parallel.
    Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."

    Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.

    Something to consider.. save a few bucks now, and pay large bucks later.
    Flickit's Avatar
    Flickit Posts: 278, Reputation: 2
    Full Member
     
    #6

    Apr 13, 2005, 07:53 PM
    Thanks for the...
    Quote Originally Posted by tkrussell
    Per the current edition of the National Electric Code:

    "Section 310.4 Conductors in Parallel.
    Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit conductor, shall be permitted to be connected in parallel (electrically joined at both ends to form a single conductor)."

    Should you install electric wiring without proper licenses or permits, and loss of life and/or property occurs due to improper installation, you insurance will not cover your losses.

    Something to consider..save a few bucks now, and pay large bucks later.
    ... info and the reminder of just how dangerous electricity is!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Neutral wire is hot(has voltage potential like the black wire) [ 5 Answers ]

Hi, The problem started at midnight last week. One of my line in the basement is starting to have issue whenever I connect a water pump or appliances to the outlets. Before I plug the appliance in, the neutral is neutral(zero voltage), but when I plug the appliance in, the neutral is now...

3-wire home, 3-wire fan, 2-wire remote [ 9 Answers ]

Greetings, My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use... The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?

2 Wire White-Rogers with no wallplate wire question [ 2 Answers ]

Hi there. I want to replace my current White-Rogers 1E56W309 thermostat with a new Honeywell RTH7500D. The problem is that the tools that installed my high efficiency furnace didn't install the wall plate with my thermostat (it was a new house and the builder contracted these guys). Instead,...


View more questions Search