Ask Experts Questions for FREE Help !
Ask
    electricguy's Avatar
    electricguy Posts: 2, Reputation: 1
    New Member
     
    #1

    Sep 11, 2010, 09:55 PM
    200 amp square d breaker and panel
    Im installing a 200 amp square d panel, but Im having a problem, the main services entrance wires comes in from ground up and the panel is made to feed from top down. I invert the panel but now my main breaker is up side down the on is on the bottom and the off is on top. Here's the question does it hamper anything with the main breaker if I also invert that so the main breaker is up right and not to the eye looking upsde down.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 12, 2010, 04:44 AM
    Circuit breakers mounted vertically shall have the on position in the up position.

    This is why they make panelboards with main breakers laying horizontally , to allow for inverting the panel for top or bottom feed.

    In your case, you need to have the breaker at the top , so the breaker handle is up for on and down for off, and need to extend the wires.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Sep 12, 2010, 05:28 AM

    How old is that panel? I can't remember that last time I saw a new single phase panel with an up-down main breaker.
    Are you re-using an old one?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Sep 12, 2010, 06:46 PM

    Electricguy,

    Please respond to a post by using the "Answer this question" section rather than the "Agree/Disagree" block.

    As to your question about the 2008 NEC, the answer is yes.

    The article you are looking for is in Part VII of Article 240. The cite you are looking for is Article 240.81 "Indicating"

    What is the part number of your panelboard so that I can look up the specifications.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

Can I put a 150 amp breaker in a 200 amp panel to feed a 150 amp sub panel? [ 8 Answers ]

Can I put a 150 amp breaker in a 200 amp panel to feed a 150 amp sub panel with a 200 amp service?

200 amp main feeding 200 amp sub-panel [ 13 Answers ]

The utility spotter recommendeds the corner of my house as the location for a 200 amp aerial service entrance/meter base. My county requires a shut-off switch with the meter base, so a combination meterbase and load center is the standard here. I'm okay with her recommended SE location, but...

Extending 200 amp service to another 200 amp panel [ 1 Answers ]

Hello Everyone, As I just found this site this is my first time posting. I am in the process of doing an addition to my home and I am having the electrical service moved as the addition is on an exterior wall. I installed a new 200 amp panel and I need to extend the electrical over to my...


View more questions Search