    Wiring and breaker for AC
    Hi, I have a wall mounted air conditioner that's 21,300 BTU, 240 volts and 13 amps. (as read on the plate). Is this OK to be on a 2 pole 20 amp breaker with 12 gauge wire. It's a dedicated circuit that runs about 25 feet. Thanks for any help
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Aug 31, 2010, 06:58 PM

    Should be OK. Even if you downrate some for possibly running quite a bit and take some voltage drop, 20 works out.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Sep 1, 2010, 02:38 AM
    The nameplate should also state MCA, Minimum Circuit Amps, to size the wire, and max fuse or breaker size.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #4

    Sep 1, 2010, 04:08 AM

    Thanks for the responses, tk, I thought that info should be on the plate, I'll take a closer look this morning.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #5

    Sep 1, 2010, 06:56 AM
    I checked the plate again and that info is not on it. Just has what I posted first time.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Sep 1, 2010, 07:10 AM
    Is this a new unit? Make and model number? May be in the datasheet or manufacturers instrucitons, should be on the nameplate thou.

    Maybe plug in units are different.

    You can go by the male plug also, but somewhere in the manufacturers documentaion should be what size circuit is needed.

    By the way, I agree with Ma0614, I am just mentioning how a circuit should be rated for an AC unit.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #7

    Sep 1, 2010, 08:38 AM

    Tk, this is an old unit, no paper work available at all, this is in the upgrade you assisted in a week or so ago. It was wired with 10/3 on the outside wall of the house and the old cable will not reach the new 200 amp service, just trying to make sure I'm right when I fish through the walls. Thanks again for the help, inspector was impressed.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Sep 1, 2010, 08:40 AM
    OK I meant to mention if it was an older unit, nameplates were done differently then.

    Impressing an inspector is always a good thing. Well done.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #9

    Sep 1, 2010, 10:23 AM

    Had to spread the rep, Well done on your part. Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

220 circuit breaker wiring [ 2 Answers ]

I had a qualified electrition install the wiring in my shop. Everything works fine, but when I tried to use a 220v planer, the first time to use the 220, nothing happens. Can it be a new but bad circuit breaker?

Wiring 50 amp breaker [ 2 Answers ]

Good Afternoon, I had a chance to acquire some 6-2 w/g and would like to know if this is okay to wire my 50 amp plug to my welder? If this is okay to use; where would the bare ground wire be connected in the sub-panel. If it is suppose to be the common, would it be wired to the common strap in the...

GFCI breaker wiring [ 10 Answers ]

I hired someone yesterday to install a gfci on the circuit that my pool lights and small backyard office are on. My home has a GTE sylvania box which uses those zinsco breakers and the gfci breaker for this panel is almost $300 each. So he ran a small box next to it, powered the box off the 20amp...

Breaker wiring [ 1 Answers ]

What kind of wire do I need for a 250 amp breaker?

Water Heater; Breaker Wiring? [ 1 Answers ]

:confused: I'm installing a new electric water heater. All plumbed and wired to the heater. Just picked up a new 30amp breaker, ready to put in the panel. 10/2 wire…At the tank; red to white, black to black, green grounded. My question is about wires to the breaker? Green is easy that’s the...


View more questions Search