    Can you use two 14 gauge wires in place of a 12 gauge?
    With a 20A circuit breaker to one 20-amp GFCI receptacle, can I use two 14 gauge wires, (that are already there), in place of a 12 gauge?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Aug 28, 2010, 03:14 PM

    Absolutely NOT!

    To use a 20 amp circuit, the cable must be 12 AWG copper.

    If any part of the circuit is using 14 AWG cable it is a violation of the NEC code and a severe fire hazard to use a 20 ampbreaker and device.

    14 AWG copper wiring can only carry a maximum of 15 amps. 12 AWG AL wire is also listed for 15 amps MAX!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Aug 28, 2010, 03:29 PM

    Absolutely NO!

    You CANNOT parallel #14 wire to use on a 20A circuit.

    What do you mean the #14 is "already there"? Is this an existing circuit?
    pacas's Avatar
    pacas Posts: 2, Reputation: 1
    New Member
     
    #4

    Aug 28, 2010, 04:57 PM

    Thanks again for the replies - Stanfortyman - no its not in an existing circuit. Just happen to have two 14 gauge wires pulled from the panel to that location and won't be used for anything. Was hoping I wouldn't have to open up the wall to pull a 12 gauge. Thanks again!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

How far can I run 240v 30 amps in a 10 gauge or 8 gauge line? [ 4 Answers ]

I'm supplying electric to a remote building with no other power source. The generator supplies 240v 30 amp. How far away can I keep the generator outside with a 10 gauge line connecting to a service panel? What if I use 8 gauge? The building is used infrequently and I run an air compressor a few...

Is it OK if a 15 amp circuit uses a 14 gauge hot but a 12 gauge neutral? [ 2 Answers ]

I've noticed some circuits in my home are on 15 amp breakers and are using 14 gauge for the hot wire but 12 gauge for the neutral wire. Is this OK?

My belly button is a 16 gauge, I put another ring in it that's a 15 gauge. [ 2 Answers ]

I got my belly button pierced about three weeks ago. I got pierced with a 16 gauge. I can't find any body jewerly that is a 16 gauge, so I decided to put a size 14 gauge in. Will it affect me in anyway? What are the effects of putting a bigger gauge in then what you were pierced with?

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...


View more questions Search