    4 wire urd
    I think I have it figured out but want to review. I can run 4 wire urd direct bury ( not a good choice but can) from remote meter base/ disconnect 200amp. As long as I run some conduit from disconnect to trench and again from trench to conduit through LB and conduit to panel I'm good. I can use urd to panel direct as long as I run in conduit not exposed coming through wall. Use LB's and conduit?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 26, 2010, 02:30 AM
    Yes the URD needs to be protected by conduit where exposed above ground. The conduit needs to be fitted with the proper connectors, locknuts, etc where connecting to there meter and panel.

    If an LB is needed, then the twist of the wires should be straightened out to help with pulling through the LB.
    meddles1's Avatar
    meddles1 Posts: 5, Reputation: 1
    New Member
     
    #3

    Aug 26, 2010, 12:34 PM

    Will 2" work or I need 2 1/2" big jump in prices.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Aug 26, 2010, 01:57 PM
    Not sure, I have no idea what size URD you have. If #4/0 Aluminum, you may need 3 inch.

    If it is #4/0, you will find that 2 inch too small, due to the twist of the URD, even thou 2" PVC Sch 40 can handle 5 #4/0 XHHW.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Should aluminum urd be buried in a conduit [ 1 Answers ]

I'm putting power into an small barn (about 40 amps) -- 300 feet from the house main panel. I want to use #6 Al URD to save $$ instead of 6-3 Direct Burial. Does the #6 Al URD need to be put in a conduit? Can I run it panel to panel?

What type #6-3 alum. Wire from my main service across the basement to aluminum URD [ 1 Answers ]

The URD is in 2" metal conduit. It services a 50 amp detached garage.What type aluminum wire should be used between the main panel, and the junction box located at the "service" side of the conduit in the basement? Can I run aluminum through the basement in "free air"? ...

What type #6-3 alum. Wire from my main service across the basement to aluminum URD [ 0 Answers ]

The URD is in 2" metal conduit. It services a 50 amp detached garage.What type aluminum wire should be used between the main panel, and the junction box located at the "service" side of the conduit in the basement? Can I run aluminum through the basement in "free air"?

What is urd wire [ 6 Answers ]

What does the type URD stand for. I know we use it for direct burial. And I was wondering what it meant. Thanks STARLITE