    burch9901 Posts: 3, Reputation: 1
    New Member
     
    #1

    Aug 7, 2010, 07:59 AM
    My Bryant AC keeps tripping the brkr. It is 4yrs old and has new capacitor and brkr.
    After I reset the breaker my unit will run through a cycle and shut off, when the stat calls for it to start up again the breaker will trip. I had the capacitor replaced last summer and it still looks fine. I replaced the 2-pole 30amp breaker yesterday. It is a bryant model: 661c. Any suggestions would be appreciated. Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Aug 7, 2010, 08:42 AM
    Quote Originally Posted by burch9901 View Post
    After I reset the breaker my unit will run through a cycle and shut off, when the stat calls for it to start up again the breaker will trip. I had the capacitor replaced last summer and it still looks fine. I replaced the 2-pole 30amp breaker yesterday. It is a bryant model: 661c. Any suggestions would be appreciated. Thanks.
    Check all high voltage (220/240 volt) connections in the entire supply side for the outside unit. Panel,outside disconnect,contact in unit etc.

    Since you have already replaced the run capacitor in the outside unit you might try a hard start kit to see if that helps the situation since you might be experiencing low power voltage in your area due to the heat and demand on the local utility. Years ago I used to just put one on for a few days just to see if it helped the situation. If not remove the hard start and seek further into the problem. You probably do not have an Amprobe to test the current draw of the unit and the individual components but if you do then use that tool to help isolate the problem.
    burch9901's Avatar
    burch9901 Posts: 3, Reputation: 1
    New Member
     
    #3

    Aug 7, 2010, 09:36 AM

    Thanks for the advice. I will try the hard start first. All of the connections looked good and I cleaned the coils and everything else out around the unit but still no luck. I will let you know what I find out. Thanks again.
    burch9901's Avatar
    burch9901 Posts: 3, Reputation: 1
    New Member
     
    #4

    Aug 11, 2010, 02:40 PM

    I installed a hard start unit and it has been working for two days now with no problems. Thanks for the advice.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Aug 11, 2010, 03:23 PM
    Quote Originally Posted by burch9901 View Post
    Thanks for the advice. I will try the hard start first. All of the connections looked good and I cleaned the coils and everything else out around the unit but still no luck. I will let you know what I find out. Thanks again.

    If it worked for 2 days it should be OK. Glad you got it working.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Start capacitor/ run capacitor info [ 3 Answers ]

OK I think I have narrowed my problem down to either a run capacitor or my start capacitor My fan on top of my unit runs but the compressor will hum for about 3-5 seconds every 5 minutes or so . Is it possible for my duel run capacitor to let the fan run but not let the compressor run, or is...

Bryant Heat Pump Capacitor [ 6 Answers ]

The capacitor on my bryant heat pump was bad and I got a new one. 1) the new one is oval and the old one was round. Is it OK if I use this new one or should I try to buy a round one as well? 2) there are three different color wires so when I discoonected the old capacitor, I did not write down...

To determine the size amp brkr. For a 5kw a/c unit do I just divide 238 (v.) by 5000 [ 4 Answers ]

To determine the size amp brkr. For a 5kw a/c unit do I just divide 238 (v.) by 5000

Installed recessed lt, addd brkr, light goes low frequently [ 4 Answers ]

Hi We installed recessed light(6), run through new circuit breaker. Now frequently when fridge automatically triggers, all house light dims and come back normal. This happen almost every 5 minutes. Before it newer used to happen. Please suggest what to do


View more questions Search