    Running power over a long distance?
    We have a 100A main feed at the road, I have a 2 - garages within 2000' of it. I need to ppower each garage. I have 8/4 cable at my disposal, and have 100A sub boxes at each garage. Does each sub need its own grounding rod? And do I isolate each sub's neutral?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 29, 2010, 11:02 AM
    My answers to your questions and comments are in red.

    I have 8/4 cable at my disposal, and have 100A sub boxes at each garage.


    Does each sub need its own grounding rod? YES.

    And do I isolate each sub's neutral? YES.

    I have 8/4 cable at my disposal. #8 is too small to deliver 120 volts 2000 feet.

    # 8/4 cable is only good for 40 amps max, and assuming a 40 amp 120 volt load, the max distance would be about 65 feet.

    At this distance of 2000 feet, transformers should be used to deliver 480 volts, at least, this distance.

    To do accurate voltage drop calculations, the maximum amperage load is needed, along with accurate distances.

    You really need to re-think your plan.
    bubble_up's Avatar
    bubble_up Posts: 5, Reputation: 1
    New Member
     
    #3

    Jul 29, 2010, 11:33 AM

    I may be overstaing the 2000' - I will get a better measurement, but what plan would you advise to me?
    bubble_up's Avatar
    bubble_up Posts: 5, Reputation: 1
    New Member
     
    #4

    Jul 29, 2010, 11:36 AM
    Quote Originally Posted by bubble_up View Post
    I may be overstating the 2000' - I will get a better measurement, but what plan would you advise to me?
    It may be within 750' to 1000' - I know it's a long way, but the original service only has #6 coming in from the meter...
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Jul 29, 2010, 06:30 PM

    Call the power company. You need more than just a bunch of cable to do what you want. Have the service brought to the building.
    bubble_up's Avatar
    bubble_up Posts: 5, Reputation: 1
    New Member
     
    #6

    Jul 30, 2010, 01:42 PM

    Sorry Missouri Bound- that would be the wise thing to do, but it's not in the budget.

    I measured it today at 650' to the 1st garage, and an additional 200' to the second garage. I just want to split the 100 A service between the 2 garages - simple fans & lighting + 1 small air compressor
    (15A @ 240V)
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #7

    Jul 30, 2010, 02:14 PM

    Well... to the first building. Assume you use a dbl pole 50A breaker... you would need 2/0 copper for that installation alone. 100amp dble pole would require 500 mmca wire. After you price that, you may reconsider calling the power company.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Jul 30, 2010, 02:37 PM
    Quote Originally Posted by bubble_up View Post
    Sorry Missouri Bound- that would be the wise thing to do, but it's not in the budget.
    Is it in the budget to do it wrong and have to re-do it?
    Or do it wrong and burn up equipment because you are only getting 90 volts?
    If doing it right is not in the budget don't do it at all.




    Quote Originally Posted by Missouri Bound View Post
    Well...to the first building. Assume you use a dbl pole 50A breaker...you would need 2/0 copper for that installation alone. 100amp dble pole would require 500 mmca wire. After you price that, you may reconsider calling the power company.
    I completely agree.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #9

    Jul 31, 2010, 03:20 AM
    All we can do is give advice to a particular questions or situation. Our advice does not need to be considered. If someone does not want to follow our advice for whatever reason, that is their decision.

    The Ohm's Law will always win.
    bubble_up's Avatar
    bubble_up Posts: 5, Reputation: 1
    New Member
     
    #10

    Aug 2, 2010, 04:42 PM

    Thank you all for the input... We hired a local licensed electrician, it wasn't that bad of a deal...
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #11

    Aug 2, 2010, 05:09 PM

    Enlighten us and please elaborate as to what the electrician plans to do for you. I, for one, am interested in the route you take.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How long is too long for a long distance relationship? [ 8 Answers ]

I am in LDR hell here, or so it seems.. before we were long distance, my boyfriend and I had been together for 3 months. It doesn't really seem that long but we were so close and I had the best time with him. So anyhow, he went off to Florida to start college in August this summer. At first,...

Running electrical wire long distance [ 2 Answers ]

I would like to know if there is any way to run 120vac to a small hunting cabin for lights. I have access to a 120vac source at a 30amp breaker box but it is 2500ft away I am tired of using a generator with the noise and keeping gas replenished. Are there any inverters or boosters, transformers etc...

Long distance running [ 3 Answers ]

I am trying to train for distance running but I'm not really sure what my workout should be. I am the type of person who needs a set workout... any suggestions

Running power to garage and continuing the power to a cabin later. [ 4 Answers ]

I'm building a garage this year and a cabin in the following years and I need to run power to the garage before building it. The service is about 60 feet away from the main breaker location and when I build the cabin, I would like to be able to continue the power from the garage to the cabin (120...


View more questions Search