    Arc fault breaker continues to trip
    I recently installed some canned lights and an arc fault breaker. When I hooked everything up, put a light bulb in one of the lights and then turned on the breaker the breaker popped. There is a 3 way switch--7 recessed lights and another 3 way switch with the power coming in to the first 3 way. If I disconnect the coiled neutral, from the arc fault breaker, from the neutral bus bar everything is fine. I checked the neutral from the arc fault breaker with a ohm meter (coiled neutral to ground bar) and I get a reading of about 113 volts. The neutral from the switch circuit shows no voltage. I checked the wiring to the arc fault breaker and it was connected correctly. Do I have a short somewher in the wiring. Not sure what to do. Any help would be greatly appriciated. Thanks
    Jannie1's Avatar
    Jannie1 Posts: 4, Reputation: 1
    New Member
     
    #2

    Jul 15, 2010, 07:06 AM
    It seem you need your local electrician.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jul 15, 2010, 07:24 AM

    It certainly sounds like a direct short to ground (ground fault).

    Leave the breaker in the off position and work from the lamp you tested back toward the breaker look for bare connectors touching metal or each other.

    Three way switches have a feed and two travelers. Switches do not have a Neutral conductor.

    You can get a book from the library or Lowe's, Home Depot etc. that will show you how to do basic switch wiring.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Arc fault breaker [ 9 Answers ]

As some of you might remember, I have knob and tube in my house. I just had a new panel installed, but the knob and tube remains. I am in the process to change that over, but in the meantime, would an AFCI breaker protect from arcs that might happen in the wall cavity? My wife heard a story of a...

ARC Fault Breaker problems [ 1 Answers ]

The ARC Fault Breaker of one of my bedrooms turns off. I cannot turn it on now. What could be the cause? By the way, I have turned off all the switches. What should I do from this point on? A related interesting question is why the night light that I plugged into one outlet in the bedroom is...

Re-setting Arc Fault Breaker [ 2 Answers ]

After an electrical storm where elec service was interupted I can not re-set the two Bedroom Arc Fault Breakers. Breakers are mfd by Eaton & has small yellow test button on each. Says type BYAF. All else is well. Home is 1 year old in Florida. Please help.

Arc fault breaker wiring [ 1 Answers ]

Can I power two arc fault protected circuits through one 14-3 feeder? I intend to install two arc fault breakers in the panel and route the power to two bedrooms through a single run of 14-3 cable.

Arc fault circuit breaker [ 5 Answers ]

I am in a high rise condo building. My bedrooms(2) arc fault circuit breaker (1) seems to be in off position (the 15amp switch) after the power in my 2 bedrooms went out quietly during the day. However, I cannot move the 15 amp switch back to the 'on' position. What is the likely problem?


View more questions Search